Issue
- With the standard real-time data retrieval from controllers using Node Red or EcoStruxure Operator Terminal Expert, we must add Modbus addresses to Unity Pro/EcoStruxure Control Expert variables. This increases the deployment time and effort considering that there may be iterations leading to the final variable list.
- Since Modbus deals natively with bytes, and the Modbus nodes generally provide data in 16-bit numbers (int, word), they must be further converted to 32-bit types using additional nodes or JS functions. Bit extraction from words also need separate nodes.
- Often WiFi media is used to connect the EcoStruxure Augmented Operator Advisor App on a tablet to the EcoStruxure Augmented Operator Advisor runtime. The WiFi network and/or WiFi devices may not be secure. Hence, these must be placed in an untrusted zone separated from the trusted SCADA+Controller zone by a firewall. Incoming connections from untrusted zones to trusted zones should be avoided. Outgoing connections from the trusted zone to untrusted zones can be allowed and must be monitored.
- To protect the controller from accidental/malicious Modbus commands, a deep packet inspection firewall (E.g. Tofino) is required.
Resolution
As a proof-of-concept, this article proposes to write real-time data from CItect SCADA to the EcoStruxure Augmented Operator Advisor Runtime via HTTP/json commands. This approach can mitigate the issues described above.