Informational UPS Events

UPS Events

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • SmartConnect
  • UPS monitoring
  • UPS Events
  • Informational UPS Events
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • EcoStruxure IT forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

SmartConnect Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to UPS Events
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
143049 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Informational UPS Events

Commander CDiggin Commander
‎2024-03-11 10:05 AM

Last Updated: Lt. Commander LFleming Lt. Commander ‎2024-11-04 06:42 AM

An Informational event does not require attention. These events are displayed in the Event Log page of the Web Portal and are for informational purposes only.

 

Informational UPS Events

  • Advanced Plan Enabled
  • Advanced Plan Expired on [date]
  • Advanced Plan Expires on [date]
  • Advanced Plan Renewed
  • Advanced Plan Expired, Standard Plan Enabled
  • Battery Connected
  • Battery Replaced
  • Battery Replacement Due
  • Communications Established
  • Standard Plan Expired on [date]
  • Standard Plan Expires on [date]
  • Standard Plan Renewed
  • Power Restored
  • Return from Bypass
  • Runtime Calibration Initiated, UPS On Battery
  • Time-On-Battery load shedding is enabled on Group X
  • TimeOnBattery Load Shedding enabled
  • TimeOnBattery Load Shedding disabled
  • UPS Command (Reboot) Accepted
  • UPS Command (Reboot) Issued for Outlet Groups: [Outlet Group]
  • UPS Firmware Upgrade in Progress
  • UPS Firmware Version Up to Date
  • UPS On
  • UPS Output Power Turned Off
  • UPS Shutdown
  • Warranty Expired on [date]
  • Warranty Expires on [date]
  • Warranty Renewed
Event
Description
Action
Advanced Plan Enabled
You have successfully purchased an Advanced plan.
No action required.
Advanced Plan Expired on [date] The expiry date of your Advanced plan has been reached. Buy a Standard or Advanced plan from Schneider Electric Exchange or a local reseller.
Advanced Plan Expires on [date] Your Advanced plan is due to expire in a number of days. You will be notified of this event on the day of expiration.  Buy a Standard or Advanced plan from Schneider Electric Exchange or a local reseller.
Advanced Plan Renewed You have successfully renewed an Advanced plan. No action required.
Advanced Plan Expired, Standard Plan Enabled An Advanced plan has expired and a previously purchased Standard Plan has been enabled. Buy an Advanced plan from Schneider Electric Exchange or a local reseller if required.
Battery Connected The UPS battery is connected and operating normally. This event is shown in the event log when the Battery Disconnected event has been resolved. No action required.
Battery Replaced A UPS battery has been replaced, and reconnected. This event is shown in the event log when the Battery Replacement Due or Battery End of Lice Exceeded events have been resolved. No action required.
Battery Replacement Due
The Web Portal has detected that the UPS battery will reach the end of its life at the date specified. The Web Portal will notify you of this impending expiry at intervals of 90, 30 and 7 days in advance of the expiry date. You will also be notified of this event on the day of expiry.
NOTE:  This is a Lifecycle Event

Buy a replacement battery cartridge by  visiting  www.apc.com  or contacting your reseller partner. If configured, your reseller will be notified when your UPS battery is due to expire. 

Communications Established
Network communications between the Web Portal and the UPS have been established. This event is shown in the event log when the Communications Lost event has been resolved.

No action required.

Standard Plan Expired on [date]
The expiry date of your Standard plan has been reached and your device is set to Basic Monitoring. 

Buy a Standard or Advanced plan from Schneider Electric Exchange or a local reseller.

Standard Plan Expires on [date]
Your Standard plan is due to expire in a number of days. You will be notified of this event on the day of expiration.

Buy a Standard or Advanced plan from Schneider Electric Exchange or a local reseller.

Standard Plan Renewed
Your Standard plan was successfully renewed. This event is shown in the event log when a Standard plan is purchased via Schneider Electric Exchange or a local reseller.

No action required.

Power Restored
The input AC utility power has returned, for example after a power outage. This event is shown in the event log when a UPS On Battery returns to an On Line state.

No action required.

Return from Bypass
The UPS is no longer in a bypass state, and the connected devices are supported by the UPS input power. This event is shown in the event log when the UPS Initiated Bypass and User Initiated Bypass events have been resolved.

No action required.

Runtime Calibration Initiated, UPS On Battery
A battery calibration has been manually initiated via the UPS LCD or PowerChute Serial Shutdown to determine an accurate reading of battery runtime available. During the runtime calibration, the devices connected to the UPS are supported by the battery. See Knowledge Base article  FA284198 for more information.

No action required.

Time-On-Battery load shedding is enabled on Group X
The UPS is on battery and load shedding is enabled on the specified group.

No action required.

TimeOnBattery Load Shedding enabled
You have enabled Load Shedding through the SmartConnect control panel.

No action required.

TimeOnBattery Load Shedding disabled
You have disabled Load Shedding through the SmartConnect control panel.

No action required.

UPS Command (Reboot) Accepted
The UPS device’s outlet group(s) reboot was successfully initiated.

No action required. 

UPS Command (Reboot) Issued for Outlet Groups: [Outlet Group]
APC Smart-UPS has initiated a reboot of the UPS device’s outlet group(s): Main Outlet Group and/or Controlled Outlet Group(s).

No action required.

UPS Firmware Upgrade in Progress
The UPS firmware update is in progress.

No action required.

UPS Firmware Version Up to Date
The UPS firmware is up to date, and no new firmware upgrade is available at this time. 

No action required.

UPS On

The UPS output power has been turned back on, and any connected devices are supported by the output power.

No action required.

UPS Output Power Turned Off

The UPS output is turned off and is not supplying power to the connected devices. 

You must turn on power to the UPS using the LCD display to supply power to devices connected to the UPS and to clear this event.

UPS Shutdown
The UPS is shutting down due to one of the following external events:
  • The option to turn the UPS Off with Delay has been selected via the UPS LCD.
  • PowerChute Network Shutdown or PowerChute Serial Shutdown has issued a command to shut down the UPS.
  • The UPS has Load Shedding configured to shut down outlet groups during an On Battery event or in response to an overload, and the Master Outlet Group has turned off.
  • The UPS has received a command to shut down via the Network Management Card Web UI, Command Line Interface, or via Simple Network Management Protocol (SNMP).
If the UPS is managed by PowerChute, it will gracefully shut down devices connected to the UPS once a shutdown sequence is configured.
 
If your UPS is not managed by PowerChute, the output power from the UPS to the connected devices is turned off, and devices connected to the UPS are not shut down gracefully.
 
To prevent this, configure a shutdown sequence using PowerChute.

 

Warranty Expired on [date]
The specified warranty end date has been reached.
NOTE: This is a Lifecycle Event

Buy an extended warranty from APC. See UPS Warranty Extension for details on extending your warranty. 

Warranty Expires on [date]
The UPS warranty is due to expire in a number of days. You will be notified of this event on the day of expiration. 
NOTE: This is a Lifecycle Event

Buy an extended warranty from APC. See UPS Warranty Extension for details on extending your warranty. 

Warranty Renewed
The UPS Warranty end date has been updated on the UPS Status > UPS Warranty page.

Contact APC Customer Support  in the event of issues with your UPS

Link copied. Please paste this link to share this article on your social media post.

Didn't find what you are looking for? Ask our Experts
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of