Critical UPS Events

UPS Events

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • SmartConnect
  • UPS monitoring
  • UPS Events
  • Critical UPS Events
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Event Types
  • Critical UPS Events
  • Warning UPS Events
  • Informational UPS Events
  • Event Types
  • Critical UPS Events
  • Warning UPS Events
  • Informational UPS Events

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

SmartConnect Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to UPS Events
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes
260412 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Critical UPS Events

Commander CDiggin Commander
‎2024-03-14 10:21 AM

Last Updated: Lt. Commander LFleming Lt. Commander ‎2024-11-04 03:33 AM

A Critical event is an event that requires immediate attention. These events are displayed in the Event Log page of the Web Portal.

 

  • Battery Disconnected
  • Battery: High Temperature
  • Battery: Temperature Threshold Exceeded
  • Communications Lost
  • Replace Battery
  • UPS Fault (Error Code)
  • UPS Initiated Bypass
  • UPS Low Battery
  • UPS Overload

Critical UPS Events

Event Description Action
Battery Disconnected The Web Portal has detected that the UPS battery has been disconnected from the UPS, and the UPS cannot support its load. Refer to the UPS Installation Guide for instructions on reconnecting the battery.
Battery: High Temperature The Web Portal has detected that the UPS battery temperature is too high. This temperature event can be caused by a high temperature at the UPS installation site, or as an early notification of an impending battery issue. Battery lifespan is impacted by the operating temperature of the battery. The optimum operating temperature for a lead-acid battery is 25º Celsius/ 77º Fahrenheit.
Take immediate steps to reduce the internal temperature of the UPS:
• Ensure sure that the UPS is installed in a cool, dry location. Check that the ambient temperature of the UPS installation site does not exceed 24º Celsius/ 75º Fahrenheit.
• Ensure that the UPS vents are not blocked, and allow a minimum of 2 inches of space around the UPS for ventilation.
• Disconnect all devices from the UPS, turn off the UPS, and cool the battery to less than 45º Celsius/ 113º Fahrenheit to clear the event. 
• Turn on the UPS and run a self test. If the self test does not pass, a replacement battery may be required.
Continued operation under this condition may result in a more critical condition. If the event persists, contact APC Customer Support for further guidance.
Battery: Temperature Threshold Exceeded
Immediate attention is required. The UPS internal battery temperature is too high and the battery may be damaged due to excess heat.
NOTE: The UPS load is not supported during this Battery Temperature event. In the event of a power outage, connected devices will not be supported by the UPS battery, and will not be shut down gracefully.
Follow the instructions in the UPS Installation Guide to immediately inspect the UPS battery.
• If the UPS battery is not swollen, or hot to the touch:
a .Promptly disconnect the battery from the UPS.
b. Contact APC Customer Support  to obtain a replacement battery.
• If the UPS battery has swollen due to excess heat and cannot be disconnected or removed from the UPS:
a. Gracefully shut down and disconnect devices connected to the UPS.
b. Turn off the UPS and disconnect input power to the UPS.
Communications Lost There have been no network communications between the Web Portal and the UPS for more than 17 minutes.
• Check that the network cable is connected to the SmartConnect Ethernet port of the UPS.
• Check that the network cable is connected to a network switch, and make sure that the network switch has an active internet connection.
• Ensure that SmartConnect access is enabled on your UPS. This can be manually enabled via the UPS device’s LCD screen. For more information, consult your UPS manual. 
Replace Battery An internal UPS battery self test has detected that the battery can no longer support its load, and needs to be replaced. Visit www.apc.com or your reseller partner to buy a replacement battery.
UPS Fault (Error Code) The UPS is reporting a hardware error. An associated Error Code is displayed to specify the type of hardware error. Contact APC Customer Support, and specify the error code displayed in the Web Portal for further assistance.
UPS Initiated Bypass The UPS is reporting an internal hardware issue that has caused the UPS to switch to bypass operation.
The action required depends on the type of hardware issue that causes the bypass. The event causing the bypass condition is also logged to the event log, e.g. UPS Fault (Error Code. Refer to the Operation Manual of your UPS for more information on possible causes or contact APC Customer Support  for further assistance and ensure to reference the UPS Error Code or UPS event that occurred at the time the UPS initiated the bypass condition.
NOTE: While in bypass, the battery is not supporting the load. If a power outage occurs, the devices connected to the UPS are not protected by the UPS battery.
UPS Low Battery The UPS operating on battery power has reached the Low Battery threshold, which is configurable via the UPS LCD, and via PowerChute Serial Shutdown. When the runtime remaining of a UPS on battery reaches this threshold, a low battery condition is triggered, and if input power is not supplied to the UPS, the UPS will shut down when the battery is exhausted. A low battery warning will also trigger a shutdown of any devices connected to the UPS that are managed by PowerChute Serial Shutdown or Network Shutdown. If devices connected to the UPS are not managed by PowerChute, gracefully shut them down immediately. Restore utility power to the UPS when the power outage is resolved.
UPS Overload The UPS cannot supply enough power to support the number or capacity of devices connected to the UPS.
If the overload event has occurred following the addition of a new device connected to the UPS, the UPS cannot support the new load. Connect the new device to another UPS, or visit www.apc.com or your reseller partner to buy a UPS model that can support the increased load.
If the overload was not caused by connecting new loads to the UPS:
• Run a UPS self test to see if the event clears.
• If the self test is passed and the overload still exists, gracefully shut down the devices connected to the UPS, and restart the UPS.
• If the problem persists, disconnect all equipment from the UPS, restart the UPS and run a self test.
•If the overload persists, contact APC Customer Support.
If the overload has cleared, reconnect and turn on devices one at a time to determine which device caused the overload condition.

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore