Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Symmetra PX & Symmetra PX2

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • Network Management Cards
  • Network Management Card 3
  • Symmetra PX & Symmetra PX2
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

NMC Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support

Symmetra PX & Symmetra PX2

Sort by:
Date
  • Date
  • Views
  • Likes
Options
  • Subscribe
  • Bookmark
  • Invite a Friend

Release Notes for Symmetra PX and Symmetra PX2 for Firmware v2.5.0.1

The Symmetra PX and PX2 application firmware v2.5.0.1 release notes apply to the following NMC cards: AP9640 UPS Network Management Card 3 AP9641 UPS Network Management Card 3 AP9643 UPS Network Management Card 3   Affected Revision Levels   Component  File Details Symmetra PX 20/40/48/96/100/160 Series Application apc_hw21_px_2-5-0-1.nmc3 UPS Application for Symmetra PX 20/40/48/96/100/160 with AP9640/41/43.   For details on upgrading the UPS Network Management Card 3 (NMC 3) firmware, see the NMC3 User Guide.   New Features     Security Updates   The default value for Bad Login Attempts is now 5. In previous firmware versions, it was 0 (unlimited). If the number of Bad Login Attempts is exceeded, the user account will be locked out for 1 hour, or until the Super User or other admin-level account unlocks the account. The Web UI now reports "Invalid username or password" instead of "Account locked out" if the number of Bad Login Attempts is exceeded. These security updates affect all user accounts, including the Super User.   Fixed Issues     Fixed Issue   Unexpected characters are visible in the Last drop-down list in the Data Log page in the Web UI for French and Japanese. The options in the drop-down list should be 2 hours, 4 hours, 8 hours, 1 day, 2 days, 4 days, 1 week, 2 weeks, 4 weeks, and All Logs.   Known Issues     Known Issues   You cannot set a UPS name that starts with a # symbol in the General screen in the Web UI (Configuration > NMC > General). The NMC incorrectly generates a “minimum temperature threshold violation no longer exists” event when a minimum humidity threshold is cleared.   Hash Signatures   Signatures apc_hw21_px_2-5-0-1.exe MD5 0fc6a918d697d275242ff385e9ddb353 SHA-1 e3fa62b5ecffef57bfca3bd1ba0218aafdbc851a SHA-256 5bdd5960eb5eef365161a32dc662b3e369ec403adbf7f89114728e8eb4c174ac
View full article
Commander CDiggin Commander
‎2024-06-25 07:21 AM

1344 Views
Didn't find what you are looking for? Ask our Experts
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore