Wiser web interface https certificate not working

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • Re: Wiser web interface https certificate not working
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
FZetina
Commander FZetina Commander
29
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
Ozturker
Ensign Ozturker
Ensign

Posted: ‎2024-07-26 04:23 AM

0 Likes
4
1408
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-26 04:23 AM

Wiser web interface https certificate not working

Ozturker_0-1721992899492.png

Hello, web interface of Wiser LBB100100 FW:3.0.0 HW:3.1 experiencing https certificate issues. How can we generate a new certificate to make it seamlessly operating

 

Thank you

 

Best Regards

 

Türker Öztürk

 

Labels
  • Labels:
  • SpaceLYnk
  • Wiser for KNX
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2024-07-30 11:04 PM . Last Modified: ‎2024-07-30 11:11 PM

1 Like
0
1313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-30 11:04 PM

The SSL certificate must be CA signed so you need to buy it, you could create a self signed certificate with OpenSSL, upload it to the controller and add the CA certificate used to “self sign” the certificate to the trusted root of your machine running the browser.

 

But it’s highly recommended to use a CA signed certificate when deploying HTTPS and use IT to help you with this as for them this is day to day business..

See Answer In Context

Reply
Replies 4
PetrMares
Commander PetrMares Commander
Commander

Posted: ‎2024-07-29 05:45 AM

2 Likes
2
1356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-29 05:45 AM

Dear Türker,

The LSS100100 uses a self-signed certificate supplied with the product by default. If you change the communication to HTTPS, the web browser will ask you to confirm the exception in order to continue.
You can import a new certificate here System Configuration > Services > HTTP SSL Certificate. This is probably not your task as the network specialist is supposed to do this for you.

Are you asking how to create another self-signed certificate for the device itself or for the whole domain where the controllers are located? In case of creating another self-signed certificate there is no plugin/script available, at least from our side and anyway this must be configured according your network setup.

Reply
Ozturker
Ensign Ozturker
Ensign

Posted: ‎2024-07-29 12:31 PM

0 Likes
1
1328
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-29 12:31 PM

Ozturker_0-1722281370083.png

Ozturker_1-1722281409936.png

 

Thank you Petr,

 

Currently the browser is unable open the web interface of the LBB100100 FW 3.0.0 HW 3.1. Where can I find the SSL Certificate from Wiser so that I can install to System Configuration > Services > HTTP SSL Certificate?

 

Best Regards

 

Türker

Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2024-07-30 04:20 AM

1 Like
0
1327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-30 04:20 AM

Hello Ozturker,

you are unable to open it via https ... but when you go for the unsecure http-way you should be able to reach the device.

 

Kind regards
Thomas

Application Design Engineer
Reply
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2024-07-30 11:04 PM . Last Modified: ‎2024-07-30 11:11 PM

1 Like
0
1314
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-30 11:04 PM

The SSL certificate must be CA signed so you need to buy it, you could create a self signed certificate with OpenSSL, upload it to the controller and add the CA certificate used to “self sign” the certificate to the trusted root of your machine running the browser.

 

But it’s highly recommended to use a CA signed certificate when deploying HTTPS and use IT to help you with this as for them this is day to day business..

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore