When is a boolean not a boolean???
SpaceLogic KNX Forum
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • When is a boolean not a boolean???
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
60
Heribert_Dölger
31
Back to SpaceLogic KNX Forum
Si67
Si67
Cadet
Posted: ‎2024-09-30 11:32 PM
717
I am having an issue that has me stuck.
I have a script which checks a group of thermostats, if any call for heat the scrip generates a boolean to a GA.
The script works and the change to the GA shows in the logs and bus monitor etc.
The problem is that this boolean does not switch the actuator.
The weird thing is that from ETS a GA write changes the boolean and the actuator changes state.
Equally using the set value from the wiser for knx objects tab changes the GA boolean and the actuator changes state.
So why is it that a boolean generated from a script which switches a GA boolean is incapable of changing an actuator state???
  • Wiser for KNX
Erwin-vd-Zwart
Janeway
Posted: ‎2024-10-02 11:17 PM . Last Modified: ‎2024-10-03 08:28 AM
@Si67
You probably use grp.update in your script, this will write the value on IP (that is why you see it in the monitor) but not on the TP (due to the limited bandwidth on TP) so the actuator will not receive anything, change grp.update to grp.write
Thomas_Rohde
Sisko
Posted: ‎2024-10-01 11:37 PM
Hi Si67,
hmm, something seems to be wrong.
Can you share more informations like pictures, the script, your architecture etc. please?
Kind regards
Thomas
Application Design Engineer
Erwin-vd-Zwart
Janeway
@Si67