A customer has a project that contains a weather station MTN682991, which has experienced a software incompatibility, importing ETS5 project. The initial project was done in ETS3.
There is a new ETS5 Fw ... I have not found anything
Is there any solution?
BR,
Raul
Link copied. Please paste this link to share this article on your social media post.
Hello Paul
Weather station MTN682991 is using a plug-in software for configuration. ETS5 is more restrictive with plug-ins. When importing the ETS3 project into ETS5 the plug-in must be installed before the import. So you should create a new empty project and import the weather station. During this the plug-in is installed.
Afterwards you should be able to import the ETS3 project and have assess to the configuration with the plug-in.
There is no dedicated ETS5 application for the weather station. You can use the existing product database for ETS3 or ETS4.
Best regards
Heribert
Link copied. Please paste this link to share this article on your social media post.
Hello Paul
Weather station MTN682991 is using a plug-in software for configuration. ETS5 is more restrictive with plug-ins. When importing the ETS3 project into ETS5 the plug-in must be installed before the import. So you should create a new empty project and import the weather station. During this the plug-in is installed.
Afterwards you should be able to import the ETS3 project and have assess to the configuration with the plug-in.
There is no dedicated ETS5 application for the weather station. You can use the existing product database for ETS3 or ETS4.
Best regards
Heribert
Link copied. Please paste this link to share this article on your social media post.
Hi Raul,
is this topic solved or do you need still support?
In case this topic is answered please mark it accordingly
so that we can get a better view on which kind of topics are really still open.
Thanks a lot for your understanding and support.
Kind regards
Thomas