USB power management on SL

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • USB power management on SL
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SpaceLogic KNX Forum
Start a Topic
Jean-Marc
Crewman Jean-Marc
Crewman

Posted: ‎2025-07-11 06:44 AM

0 Likes
4
397
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-11 06:44 AM

USB power management on SL

Hello everyone,

I have a Lua script reading data from a Linky meter via an FT232 USB-to-serial converter connected to /dev/ttyUSB0.

My script has robust error handling and can detect communication failures, but sometimes the FT232 chip gets "stuck" and a simple USB reset is not sufficient to recover. The chip needs a complete power cycle (5V cut) to restart properly.

Currently I'm using a reset function from user library, but it only does a software USB reset which doesn't cut the 5V power supply.

Question: Is there a way from a Lua script (or system command via os.execute()) to completely cut and restore the 5V power supply to a USB port on the SL?

I've considered:

  • uhubctl (if available on SL)
  • GPIO control (if USB power is GPIO-controlled)
  • SL-specific system commands

Any suggestions or experience with this kind of USB power management on SL?

Thanks in advance!

Labels
  • Labels:
  • Wiser for KNX
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2025-07-16 11:56 PM

0 Likes
1
390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-16 11:56 PM

@Jean-Marc 
 
You can power cycle USB port like this:
 
Code:
io.writefile('/dev/usbctrl', 'low')
os.sleep(1)
io.writefile('/dev/usbctrl', 'high')
os.sleep(1)
 
Make sure that serial port is not open in a script when doing the power cycle. Otherwise the port name might change and script won't work. Also make sure to allow "unsafe scripts" in the general configuration otherwise the io.writefile is not executed.
 
If this does not work your only option is to fully restart the controller by using os.execute('reboot') but be careful with this, if you loop controller in constant reboot, the only way out of that is a full hardware factory reset, so be sure to have a recent backup before trying this.
Reply
Jean-Marc
Crewman Jean-Marc
Crewman

Posted: ‎2025-07-18 06:22 AM

0 Likes
0
372
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-18 06:22 AM

Thanks Erwin,

I already tried the function ('/dev/usb ctrl', 'low') it doesn't work. For now I use the reboot but I don't like this solution at all

 BR

Reply
Jean-Marc
Crewman Jean-Marc
Crewman

Posted: ‎2025-07-18 08:06 AM

1 Like
0
340
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-18 08:06 AM

For those who are interested, here is the solution:

function hardResetUSB()
log("Hard reset USB FT232 - Méthode authorized")

-- Déauthoriser le device USB (coupe la communication)
os.execute('echo "0" > /sys/bus/usb/devices/1-1/authorized')

-- Attendre déconnexion complète
os.execute('sleep 3')

-- Réauthoriser le device USB (reconnecte)
os.execute('echo "1" > /sys/bus/usb/devices/1-1/authorized')

-- Attendre reconnexion et re-création de /dev/ttyUSB0
os.execute('sleep 3')

log("Hard reset USB terminé - FT232 réinitialisé")
end

Reply
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2025-07-18 11:39 PM

1 Like
0
365
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-18 11:39 PM

@Jean-Marc 

 

Always target the source of the issue instead of putting bandages in place..

 

I would replace the USB dongle for a better one that probably keeps working..

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore