Hello Hannes
I checked the data base and found that all group objects for energy consumption (objects 13, 32, 51 and 70 for all 4 channels) are linked with group address 0/7/3 "ALLE TOTAL VERBRUIK RESETTEN". This group address is not linked to any other device except the switch actuators with current detection.
Is it possible that there is a device in the network that does not appear in the ETS project data base but executing a reset of the counter (for example HomeLYnk)? As the "write" flag of this group object is activated it would be possible that i.e. HomeLYnk is resetting the counter for energy consumption with the help of this group object.
This might explain why the Counter Limit of 50000 kWh is never reached.