Switch actuator + current detection - MTN647595
Hello,
We found that the switch actuator resets the energy consumption object (object 13 for channel 1)
once the value reaches +/-600kWh. The limit value however is set at 50000kWh in the parameters.
The Energy limit value reached object is never activated (object 14 for channel 1).
In attachment there's a snapshot of the parameter settings.
Kind regards,
Hannes
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Hannes
I checked the data base and found that all group objects for energy consumption (objects 13, 32, 51 and 70 for all 4 channels) are linked with group address 0/7/3 "ALLE TOTAL VERBRUIK RESETTEN". This group address is not linked to any other device except the switch actuators with current detection.
Is it possible that there is a device in the network that does not appear in the ETS project data base but executing a reset of the counter (for example HomeLYnk)? As the "write" flag of this group object is activated it would be possible that i.e. HomeLYnk is resetting the counter for energy consumption with the help of this group object.
This might explain why the Counter Limit of 50000 kWh is never reached.
Best regards
Heribert