Support on KNX Dimmer not connected with Light

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • Support on KNX Dimmer not connected with Light
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Related Products
product field
SpaceLogic KNX - 4ʺ Touch Unit
product field
KNX Push Button Dynamic Labeling, universal
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
Samimul_Islam
Lieutenant JG Samimul_Islam
Lieutenant JG

Posted: ‎2023-12-17 10:22 PM . Last Modified: ‎2024-07-14 11:41 PM

0 Likes
8
1789
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-17 10:22 PM

Support on KNX Dimmer not connected with Light

Hi

We are working on Luxury residential automation project which is Schneider KNX Based automation in Bangladesh. Customer used FLOS brand light shade with driver where we used Universal dimmer master (MTN6710-0102) in project but when pressed the button lights is ON after that lights automatically OFF with error indicator blinking.

 

Please find the following link for your more understanding.

https://drive.google.com/file/d/1foI4v0iwojiR51oridDo0rngAXX6aEmT/view?usp=sharing

 

Could you please support how to solve the problem? Customer is pressing to solve the issue.

  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
    KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (3)
Labels
  • Labels:
  • Wiser for KNX
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2023-12-19 02:20 AM

0 Likes
0
1787
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-19 02:20 AM

Hi Samimul,

 

many THANKS for the video which shows clearly the behaviour of the connected ballasts.
As the ERR-Led is just flashing ones and not permanently ... it could indicate that we have some kind of overload?!
Cutout of the product informationCutout of the product information

 

Can you double check your loads with the ones specified below?

Specified loadsSpecified loads 

Kind regards
Thomas

Application Design Engineer

See Answer In Context

Reply
Replies 8
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2023-12-19 02:20 AM

0 Likes
0
1788
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-19 02:20 AM

Hi Samimul,

 

many THANKS for the video which shows clearly the behaviour of the connected ballasts.
As the ERR-Led is just flashing ones and not permanently ... it could indicate that we have some kind of overload?!
Cutout of the product informationCutout of the product information

 

Can you double check your loads with the ones specified below?

Specified loadsSpecified loads 

Kind regards
Thomas

Application Design Engineer
Reply
Samimul_Islam
Lieutenant JG Samimul_Islam
Lieutenant JG

Posted: ‎2023-12-19 09:51 PM

0 Likes
3
1785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-19 09:51 PM

Hi Thomas,

we have checked few times lights functional ok using 2 channel  KNX dimmer later its behavior instance only ON and atomically off with error LED. When using 4 channel KNX dimmer (MTN6710-0004) lights are functional. 

 

We have supplied customer site 8 nos. 2 channel dimmer also he installed FLOS brand light. He pressurized me to solve the issue. Only Problem is 2 channel dimmer.

 

could you please share your whatsApp or others number for remote support?

 

BR

Samimul Islam

Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2023-12-21 12:40 AM

0 Likes
2
1781
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-21 12:40 AM

Hi Samimul,

 

just to be sure that I understand your actions in the right way ...
- Your lights still doesnt work with Spacelogic Dimmer Master (MTN6710-0102)

- Your lights in general ok and functional validated by the use of our 4 Channel low load dimmer (MTN6710-0004). I guess you have used only 2 out of the 4 channels ... right?

In case I am right .. then it seems the load of the used lights are to high for our Spacelogic Dimmer Master (MTN6710-0102).

Could you please share more details about your loads?

 

 

Kind regards
Thomas

Application Design Engineer
Reply
esteve_budia
Lieutenant esteve_budia Lieutenant
Lieutenant

Posted: ‎2023-12-21 10:37 PM

1 Like
0
1779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-21 10:37 PM

Hi, sometimes the problem is becouse LED lights in general on market are fully inductive and controller isn't able to detect as a correct load, sometimes is the reason of warning. If you turn on an off it works fine, but light error is reporting a problem.

One of the different solutions to improve this error is put a resistor in parallel with load like this:

esteve_budia_0-1703226770986.png

 

This is a 14kOhms 5W 230V Resistor.

The light regulation even comes more stable with it, but you are adding 3W to your channel load when using at 100%.

 

 

Reply
Samimul_Islam
Lieutenant JG Samimul_Islam
Lieutenant JG

Posted: ‎2023-12-31 08:46 PM

0 Likes
1
1774
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-31 08:46 PM

Hi Thomas,

Please see the following feedback 

1. Your lights in general ok and functional validated by the use of our 4 Channel low load dimmer (MTN6710-0004). I guess you have used only 2 out of the 4 channels ... right? Yes

2. we used LED light which each light 2.7W and 900mA  is connected Spacelogic Dimmer Master (MTN6710-0102).

Also, please see the following link for your more understanding.

https://drive.google.com/drive/folders/15HLXiYmmdQQiT95Gj8VgNVChsbZ493y6?usp=sharing

 

we need your positive support regarding this issue to solve it for our customer.

Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2024-01-03 01:44 AM

1 Like
0
1768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-03 01:44 AM

Hello Samimul,

 

I got the feedback from our development team that we faced already problems with this type of LED-Driver you are using. The recommendation is to install an external resistor in parallel. For e.g. the one mentioned above by Esteve.

 

Kind regards
Thomas

Application Design Engineer
Reply
Samimul_Islam
Lieutenant JG Samimul_Islam
Lieutenant JG

Posted: ‎2024-02-06 11:57 PM

0 Likes
1
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-02-06 11:57 PM

Hi @Thomas_Rohde  & @esteve_budia 

As per your instruction, we have tested at site and our office using resistor in parallel with lights as per below link where light is on/off and dimming perfectly but resistor is over heated can't touch hand and error is shown. we used 10Kohms 5w 220v resistor for test purpose. Because we have supplied 2CH dimmer and Flos brand lights with driver. customer always pressurized us to solve the issue.

 

Now what we will do. please suggest your valuable feedback for us.

 

https://drive.google.com/file/d/1Kz0THjHUhMbQiOdDhrPbQMYBlfd5WsK4/view?usp=sharing

 

Regards

Samimul Islam 

 

 

Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2024-02-08 05:13 AM

0 Likes
0
1574
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-02-08 05:13 AM

Hello Samimul,

 

if it doesnt work properly with the proposed resistor ...
Another option is to use a dedicated compensation module (CCT90501).

https://download.schneider-electric.com/files?p_Doc_Ref=CCT90501_IOP-front&p_File_Type=rendition_520... 

 

 

Kind regards
Thomas

Application Design Engineer
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore