Hi.
Is it possible to have Spacelynk setup as IP router on KNX between 2 KNX lines, and also act as control interface and visualisation?
In the KNX settings I have to choose mode to IP-Router and then the TP-UART doesnt write on KNX buss anymore right?
- Labels:
-
SpaceLYnk
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi,
yes. spaceLYnk can act as a KNX IP router. Filtering tables must be properly set.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi.
Yes but can it at the same time act as visualisation server with the possibility to write commands to KNX TP? Or do I have to have a seperate KNX/IP Router in this case?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi.
But can it act as a IP router and in the same installation act as a visualisation server and be able to write telegrams on KNX TP from visu widgets?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
As said before, SL is a native Controller with Webserver AND KNX/IP functionality.
What you have to do is properly set the filter table in both direction, TP>Ip and IP>TP.
You can do that directly from the KNX object view or from the KNX connection settings