SpaceLYnk - Issues on the BACnet connectivity

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • SpaceLYnk - Issues on the BACnet connectivity
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Related Products
product field
SpaceLogic KNX - 4ʺ Touch Unit
product field
KNX Push Button Dynamic Labeling, universal
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
Cristiano_Carli_Ballola
Lt. Commander Cristiano_Carli_Ballola Lt. Commander
Lt. Commander

Posted: ‎2024-01-17 02:45 AM . Last Modified: ‎2024-07-14 11:41 PM

0 Likes
4
2691
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-17 02:45 AM

SpaceLYnk - Issues on the BACnet connectivity

I'm currently facing an issue while I'm trying to detect and connect to my BACnet network a SpaceLYnk controller.
Device discovery is able to detect the device, but the BACnet name doesn't match and the Model as well as vendor name and Description are not shown.

Cristiano_Carli_Ballola_0-1705488074557.png

And this is the error message that pops-up when I'm trying to link the controller to my BACnet interface

Cristiano_Carli_Ballola_1-1705488167736.png

Unknown object
BACnet
~/BACnet Interface/IP Network/Device_1100000/BACnetName
BACnet plugin
0
ReadProperty

Unknown object
BACnet
~/BACnet Interface/IP Network/Device_1100000/BACnetName
BACnet plugin
0
ReadProperty

 

 

The Controller is a SpaceLYnk V2.0, with FW v3.0.0
The issue is not related to the firmware version; it also popped up with fw version 2.8.3

As you can see, on the same structure, I have a 2nd controller (wiser for knx) which doesn't show any issue

Cristiano_Carli_Ballola_2-1705488266473.png


Any idea on how to solve that issue?

  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
    KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (3)
Labels
  • Labels:
  • Protocols
  • SpaceLYnk
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Cristiano_Carli_Ballola
Lt. Commander Cristiano_Carli_Ballola Lt. Commander
Lt. Commander

Posted: ‎2024-01-17 08:20 AM

0 Likes
1
2652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-17 08:20 AM

UPDATE

I have deleted the BACnet Client App from the controller and, apparently, is now working correctly.

See Answer In Context

Reply
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2024-01-17 09:58 PM

0 Likes
0
2627
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-17 09:58 PM

Ah, that is normal behavior, you cannot use the client and server at the same time as they both use port 47808 and that results in a port conflict.

 

When having the BACnet client installed the server must be disabled.

 

When you want to use the server again you must delete the client app like you did now.

See Answer In Context

Reply
Replies 4
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2024-01-17 06:42 AM . Last Modified: ‎2024-01-17 06:53 AM

1 Like
3
2664
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-17 06:42 AM

There is more wrong as it also does not show the vendor name..

 

Can you try to compare the BACnet settings of both devices? Try also a different Device ID like 112233 to test if there is a conflict with it.

 

Try also to give the controller another host name (when Device name (optional) is empty) because that is used in the BACnet name.

 

Try to disable the server and than enable it before doing a new discovery or reboot the controller first.

Reply
Cristiano_Carli_Ballola
Lt. Commander Cristiano_Carli_Ballola Lt. Commander
Lt. Commander

Posted: ‎2024-01-17 07:53 AM . Last Modified: ‎2024-01-17 08:06 AM

0 Likes
0
2656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-17 07:53 AM

Hello @Erwin-vd-Zwart 
These are the BACnet setting of the working controller (Wiser for KNX)

Cristiano_Carli_Ballola_0-1705506669659.png

and these are the settings of the non working controller (SpaceLYnk)

Cristiano_Carli_Ballola_1-1705506756673.png

Do you see anything what have to be changed/modified?
BTW
After a reboot, apparently, the device is correctly listed

Cristiano_Carli_Ballola_2-1705507150734.png

but, unfortunately, the same error pops up when I try to add it to the BACnet Interface

Cristiano_Carli_Ballola_3-1705507226084.png

And if I perform a new "discover All" within the Device Discovery, the controller is listed again with the previous configuration

Cristiano_Carli_Ballola_0-1705507563854.png

 

Reply
Cristiano_Carli_Ballola
Lt. Commander Cristiano_Carli_Ballola Lt. Commander
Lt. Commander

Posted: ‎2024-01-17 08:20 AM

0 Likes
1
2653
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-17 08:20 AM

UPDATE

I have deleted the BACnet Client App from the controller and, apparently, is now working correctly.

Reply
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
Janeway

Posted: ‎2024-01-17 09:58 PM

0 Likes
0
2628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-17 09:58 PM

Ah, that is normal behavior, you cannot use the client and server at the same time as they both use port 47808 and that results in a port conflict.

 

When having the BACnet client installed the server must be disabled.

 

When you want to use the server again you must delete the client app like you did now.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore