Posted: ‎2021-11-19 06:14 AM . Last Modified: ‎2024-07-14 11:45 PM
971
Dear Experts,
we are facing problem with the integration and working of schneider multitouch pro MTN6215-5910 with knx cool master.
we need to understand the parameter setting and group address to be linked in multitouch pro.
we are able to control knx coolmaster with ets5, by sending command to cool master through group address monitoring.
the only challenge is to how to send command from multitouch pro and how its room temperature controls works and how many group addresses are needed and what are there data type.
Please support in resolving the issue
Akash Shinde
  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
View products (3)
  • Protocols
  • SpaceLogic devices
Thomas_Rohde
Sisko
Posted: ‎2021-11-22 12:08 AM
2
968
Dear
did you checked the following document?
https://download.schneider-electric.com/files?p_Doc_Ref=MTN621x-0310_5910_SW_EN&p_enDocType=System+u...
Within chapter 7 (Room temperature control unit) you will find starting by page 94 up to123 a lot of insights.
As specially on the last page (123) you will find an overview of all needed group objects.
Kind regards
Thomas
Application Design Engineer
Posted: ‎2021-12-01 01:12 AM
959
Dear Thomas,
Thank you for your support, as per the suggestion document which you have sent, we have done the programming.
We need your support for further process, can we have a call to understand the same.
I am reachable at akash.shinde@rexel.co.in
Akash Shinde
Thomas_Rohde
Sisko
Posted: ‎2021-12-06 12:56 AM
Dear Akash,
sorry for the late reply. Our local colleague Chetan Sharma will contact you to provide support.
Kind regards
Thomas