Hello
Can somebody can explain what kind of license LSS900100 ( KNX graphical software - eConfigure KNX Lite for 250 KNX devices) have please?
LSS900100 is specified as for 250 devices but ETS shows only 20 devices per project. (see attached photos)
In what sense i can add 250 devices?
LSS900100
Link copied. Please paste this link to share this article on your social media post.
eConfigure is using an ETS Lite license which allows up to 20 devices. But this ETS license is only used in the background for commissioning the devices from eConfigure. Inside eConfigure you are able to manage and commission 250 devices. For commissioning, eConfigure creates ETS project with one device, commisisons it and deletes the device again in ETS. Due to that it is possible to manage and commission up to 250 devices with eConfigure.
Link copied. Please paste this link to share this article on your social media post.
eConfigure is using an ETS Lite license which allows up to 20 devices. But this ETS license is only used in the background for commissioning the devices from eConfigure. Inside eConfigure you are able to manage and commission 250 devices. For commissioning, eConfigure creates ETS project with one device, commisisons it and deletes the device again in ETS. Due to that it is possible to manage and commission up to 250 devices with eConfigure.