LSS100100 Modbus integration with BMS

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • LSS100100 Modbus integration with BMS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
131
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
59
Heribert_Dölger
Commander Heribert_Dölger Commander
31
FZetina
Commander FZetina Commander
29
View All
Related Products
product field
SpaceLogic KNX - 4ʺ Touch Unit
product field
KNX Push Button Dynamic Labeling, universal
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
Ascentrek
Ascentrek
Cadet

Posted: ‎2021-09-05 09:43 AM . Last Modified: ‎2024-07-14 11:46 PM

0 Likes
2
732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-05 09:43 AM

LSS100100 Modbus integration with BMS

Dear team can we integrate lss100100 to bms via modbus protocol if possible pls confirm process

  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
    KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (3)
Labels
  • Labels:
  • Protocols
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
David_Navratil
Lt. Commander David_Navratil Lt. Commander
Lt. Commander

Posted: ‎2021-09-06 12:35 AM

0 Likes
0
722
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-06 12:35 AM

Hello @Ascentrek,

 

What BMS device you are about to integrate with LSS100100?

Yes it is possible. LSS100100 supports both Modbus RTU or Modbus IP.

Process is that:

1. You need Modbus profile - what is the definition of the registers from the BMS device what you will be sending/receiving over Modbus

2. If this profile is already available in the LSS100100 list of the profiles you need only to add new device with correct parameters and this profile used.

3. If the profile does not exist you have to define a new one based on the Userguide where is a description of what parameters and how the profile is defined. Also, you can download the already existing profile from the LSS100100 to see the structure and redefine it to your needs.

 

Regards

David

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
Ascentrek
Ascentrek
Cadet

Posted: ‎2021-09-05 09:49 AM

0 Likes
0
728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-05 09:49 AM

How to integrate lss100100 to bms via modbus protocol

Tags (1)
  • Tags:
  • english
Reply
David_Navratil
Lt. Commander David_Navratil Lt. Commander
Lt. Commander

Posted: ‎2021-09-06 12:35 AM

0 Likes
0
723
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-09-06 12:35 AM

Hello @Ascentrek,

 

What BMS device you are about to integrate with LSS100100?

Yes it is possible. LSS100100 supports both Modbus RTU or Modbus IP.

Process is that:

1. You need Modbus profile - what is the definition of the registers from the BMS device what you will be sending/receiving over Modbus

2. If this profile is already available in the LSS100100 list of the profiles you need only to add new device with correct parameters and this profile used.

3. If the profile does not exist you have to define a new one based on the Userguide where is a description of what parameters and how the profile is defined. Also, you can download the already existing profile from the LSS100100 to see the structure and redefine it to your needs.

 

Regards

David

Tags (1)
  • Tags:
  • english
Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore