KNX Mini presence detector MTN6303-0019 send ON Command when power reset

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • KNX Mini presence detector MTN6303-0019 send ON Command when power reset
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2024-09-04 07:59 AM

0 Likes
9
1419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-04 07:59 AM

KNX Mini presence detector MTN6303-0019 send ON Command when power reset

Hello Team,

A customer reported that the lights remained on and did not turn off after a power reset. This issue occurred because the Mini Presence sensor sent an “on” command when power outage occurred.

 

To resolve this, you can set the sensor to send the value cyclically as “off,” as shown in the image below.

The question is: Is this the normal operation?

 

Capture.PNG

 

Best Regards,
Labels
  • Labels:
  • SpaceLogic devices
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2024-09-09 01:06 AM

1 Like
0
1240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-09 01:06 AM

Hello again

 

Your test conditions are fully valid and can happen in real life. I only mentioned the difference to my test conditions because my setup didn't allow to see the ON command of the detector when KNX power disappears.

 

Unfortunately, this behaviour cannot be eliminated. It is a function inside firmware and there is no parameter to avoid it. And the detector does not have the option to load a different firmware.

See Answer In Context

Reply
Replies 9
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2024-09-05 02:45 AM

1 Like
1
1389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-05 02:45 AM

Hello

 

When the Mini Presence Sensor is powered it sends ON command and shortly afterwards OFF. So it seems in your case the switch actuator seems to react to the ON command but not to the OFF. Or the actuator is configured to go to last value after return of KNX bus voltage, and the actuator takes more time to reboot after power return and does see neither ON nor OFF and goes to the last value.

 

The configuration to send OFF value cyclically indeed would help in this situation. It is a normal setting that can be chosen.

Reply
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2024-09-05 04:59 AM . Last Modified: ‎2024-09-05 05:08 AM

0 Likes
0
1374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-05 04:59 AM

Hello @Heribert_Dölger 

I noticed that the Actuator channel receives an on command before it turn off when the power is disconnected!
means that the on command sent during power off.

Also I see that the Mini presence sent an on command then shortly afterword OFF command after application download not after power reset!
you could see the actuator failure behavior for the desired channel.

You are right the channel configured to go to last value after return of KNX bus voltage, this is the new Spacelogic Master

 

 

Capture.PNG

 

Best Regards,
Reply
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2024-09-05 05:10 AM

0 Likes
1
1371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-05 05:10 AM

With the setting of the actuator it will come back with the status before power cut. So it will be ON in case it was ON before. In my test the Mini Presence Sensor did not send ON command when I removed it from the KNX power supply. But in that moment it was not detecting presence. Maybe in your case a person was detected shortly before and due to that it had sent ON command.

 

The ON and OFF is sent after application download and power reset. Strange that you don't see it after power reset. After ETS application download the device is being reset. That's why the same behaviour appears after bus power return.

Reply
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2024-09-05 05:16 AM

0 Likes
0
1370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-05 05:16 AM

@Heribert_Dölger 
Do you test on Spacelogic Master Actuator?
I test the case on the office and blind the Motion before disconnecting the power, I noticed an on command sent to the channel during power off, I will do the test again to check.
In your case do you have the same response after power reset and application download.

 

Best Regards,
Reply
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2024-09-05 05:42 AM

0 Likes
1
1350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-05 05:42 AM

I am testing without actuator. Just looking at the telegrams on the ETS group monitor.

 

I can confirm that the ON and OFF sequence is sent after reset and application download.

 

I do not see an ON command when I cut the KNX bus power. If you have the sensor in a box and remove the KNX connector this might be seen as movement in case you move the device by that operation.

Reply
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2024-09-05 05:59 AM

0 Likes
0
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-05 05:59 AM

Please take a look on the ETS telegrams 
I did the test by tripping the circuit breaker, the actuator channel was off before test GA 1/1/137 for F/B

the on telegram couldn't be monitored during the power off while the SL still powered and monitoring the bus, but actually the actuator channel is switched on during power off, so because of that you didnt see any on telegram during the power off.

if you could make a real test with Spacelogic actuator connected.

Also, if you see that the reboot time for the Mini Presence is faster than the Spacelogic actuator, the on and off  command sent before the spacelogic even start, so this shouldnt make any issue, but the issue remain during the power off.

appreciate your effort.

Capture.PNG

 

Best Regards,
Reply
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2024-09-06 01:16 AM . Last Modified: ‎2024-09-06 01:17 AM

1 Like
0
1291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-06 01:16 AM

Indeed it makes a difference how to test. When testing like you (switch OFF the KNX power by circuit breaker) I can see that the Mini Presence detector is sending ON command. The Spacelogic switching actuator receives this command and due to that takes this as the last value.

 

Also I can confirm that the switching actuator takes more time to reboot. When power returns the Mini sensor send the ON command, few seconds later the OFF command. But the switching actuator does not see these telegrams. Shortly later switching actuator sends feedback value ON as this was the last status.

 

Configuring cyclical sending of the OFF command of the Mini sensor will help. I configured a cycle time of 5sec and the light then was switched OFF shortly after it was switched ON.

Reply
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2024-09-08 01:46 AM

0 Likes
0
1262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-08 01:46 AM

Thank you @Heribert_Dölger 

Appreciate your effort, But do you think that power reset case like power outage from the utility is not similar to switch off power by circuit breaker?

while the customer complain several time, in our countries its usual to have power outage for several minutes every month.

Is it possible to enhance the Mini presence to not send ON Command during the power off?

Best Regards,
Reply
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2024-09-09 01:06 AM

1 Like
0
1241
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-09-09 01:06 AM

Hello again

 

Your test conditions are fully valid and can happen in real life. I only mentioned the difference to my test conditions because my setup didn't allow to see the ON command of the detector when KNX power disappears.

 

Unfortunately, this behaviour cannot be eliminated. It is a function inside firmware and there is no parameter to avoid it. And the detector does not have the option to load a different firmware.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore