KNX LSS100100 - traffic lights - overload of the controller & repeats on KNX BUS (Over 600%)

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • KNX LSS100100 - traffic lights - overload of the controller & repeats on KNX BUS (Over 600%)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
121
Erwin-vd-Zwart
Sisko Erwin-vd-Zwart Sisko
54
Heribert_Dölger
Lt. Commander Heribert_Dölger Lt. Commander
30
FZetina
Lt. Commander FZetina Lt. Commander
27
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Solved
tiago_oesteprisma
Crewman tiago_oesteprisma
Crewman

Posted: ‎2024-12-17 09:48 AM

0 Likes
7
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-17 09:48 AM

KNX LSS100100 - traffic lights - overload of the controller & repeats on KNX BUS (Over 600%)

Hi,

I'm not able to remote control the installation using "wiser for knx" android app.

The app keep's loading, but the touch buttons don't appear.

The only sign of error is in the traffic lights, but I'can't see how this percentage can be reduced.

Any tips how we can reduce this in the installation?

Thanks in advance.

Attachments
Labels
  • Labels:
  • SpaceLogic devices
  • Wiser for KNX
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
esteve_budia
Lieutenant esteve_budia Lieutenant
Lieutenant

Posted: ‎2024-12-20 02:17 AM

1 Like
2
960
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-20 02:17 AM

I'd like to share with you this "Repeats Guide" to help anybody with this traffic lights problem:

esteve_budia_12-1734689008475.png

 

When we encounter this problem we must act on several guidelines:

esteve_budia_13-1734689101710.png

Use the built-in tool in Wiser to know the level of repetitions:

This Tool is located in:

Configurator / System / Network / KNX Statistics

esteve_budia_14-1734689176216.png

What to do then to ELIMINATE the repetitions?

 

1.- Eliminate shipments not recognized as orphan telegrams such as temperatures, wind speed and other telegrams that do not have an associated actuator. This can be done by activating this function:

esteve_budia_15-1734689224763.png

Configurator / System / Network / KNX Connection / Enable -> ACK in all telegroups

 

esteve_budia_16-1734689274393.png

2.- If we use Modbus profiles, it is important that all addresses here are "virtual" otherwise group addresses less than 31 would also cause repetitions.

 

3.- Limit the use of addresses smaller than 31 in the scripts and replace them with virtual addresses.

 

 

 

4.- After all this, if we still have repetitions we will have to use our USB interface to see the bus telegrams through the Bus Monitor:

esteve_budia_17-1734689390337.png

In this case, it is Wiser For KNX itself who sends unrecognized telegrams since it cannot recognize itself.

Using virtual variable, more much better.

 

 

Repetitions produced by Couplers:

-------------------------------------------

It is very important to have the IP couplers/router well configured so as not to propagate telegrams or repetitions upstream of the TP connections.

Below is an example of how to configure these devices:

 

esteve_budia_18-1734689789280.png

 

In both one direction and the other, the repetitions must be set to NO.

On the other hand, it is also more than advisable to always use the telegram filtering option using the route tables.

Today, you don't have to do anything else, the ETS configures everything for you to work.

Also remember that the couplers must be reprogrammed last and whenever we modify any element on the bus, they must be reprogrammed again to update the route tables.

See Answer In Context

Reply
Replies 7
Cristiano_Carli_Ballola
Lt. Commander Cristiano_Carli_Ballola Lt. Commander
Lt. Commander

Posted: ‎2024-12-18 11:56 PM

0 Likes
0
1008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-18 11:56 PM

That Red traffic light is most likely generated by the repeated telegramms.
Two tips to reduce that issue:
- enable the "ack all telegramms"  within the Controller settings.
- use virtual KNX object instead of classic KNX object when ever is possible, especially when that
object is used within the controller only

Reply
FZetina
Lt. Commander FZetina Lt. Commander
Lt. Commander

Posted: ‎2024-12-19 03:18 AM

0 Likes
0
998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-19 03:18 AM

Hi @tiago_oesteprisma 

 

When the app fails to load information on the screens, it is often due to the controller being overloaded, which disrupts communication with the app. A quick fix is to restart the controller; however, depending on the underlying cause, this issue may recur. To prevent this, please follow the best practices and recommendations that Cristiano highlighted (above) to ensure these factors do not impact your controller's performance.

Thank you!

Best,
Fernando

Fernando Zetina
Reply
tiago_oesteprisma
Crewman tiago_oesteprisma
Crewman

Posted: ‎2024-12-19 05:02 AM

0 Likes
0
987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-19 05:02 AM

@FZetina and @Cristiano_Carli_Ballola , thanks for your reply.

It worked, the controller has now values bellow 13%.

Although, the acess to the installation (touch,PC/Tablet/Smartphone), are very slow.

Take more than 3 minutes to access. It displays the icon in the image.

Acessing to the other options are working fine.

Any ideias?

capture.png

Reply
esteve_budia
Lieutenant esteve_budia Lieutenant
Lieutenant

Posted: ‎2024-12-20 02:17 AM

1 Like
2
961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-20 02:17 AM

I'd like to share with you this "Repeats Guide" to help anybody with this traffic lights problem:

esteve_budia_12-1734689008475.png

 

When we encounter this problem we must act on several guidelines:

esteve_budia_13-1734689101710.png

Use the built-in tool in Wiser to know the level of repetitions:

This Tool is located in:

Configurator / System / Network / KNX Statistics

esteve_budia_14-1734689176216.png

What to do then to ELIMINATE the repetitions?

 

1.- Eliminate shipments not recognized as orphan telegrams such as temperatures, wind speed and other telegrams that do not have an associated actuator. This can be done by activating this function:

esteve_budia_15-1734689224763.png

Configurator / System / Network / KNX Connection / Enable -> ACK in all telegroups

 

esteve_budia_16-1734689274393.png

2.- If we use Modbus profiles, it is important that all addresses here are "virtual" otherwise group addresses less than 31 would also cause repetitions.

 

3.- Limit the use of addresses smaller than 31 in the scripts and replace them with virtual addresses.

 

 

 

4.- After all this, if we still have repetitions we will have to use our USB interface to see the bus telegrams through the Bus Monitor:

esteve_budia_17-1734689390337.png

In this case, it is Wiser For KNX itself who sends unrecognized telegrams since it cannot recognize itself.

Using virtual variable, more much better.

 

 

Repetitions produced by Couplers:

-------------------------------------------

It is very important to have the IP couplers/router well configured so as not to propagate telegrams or repetitions upstream of the TP connections.

Below is an example of how to configure these devices:

 

esteve_budia_18-1734689789280.png

 

In both one direction and the other, the repetitions must be set to NO.

On the other hand, it is also more than advisable to always use the telegram filtering option using the route tables.

Today, you don't have to do anything else, the ETS configures everything for you to work.

Also remember that the couplers must be reprogrammed last and whenever we modify any element on the bus, they must be reprogrammed again to update the route tables.

Reply
tiago_oesteprisma
Crewman tiago_oesteprisma
Crewman

Posted: ‎2024-12-20 04:31 AM

0 Likes
1
949
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-20 04:31 AM

thanks @esteve_budia 

The tips you gave worked, and now there aren't any traffic lights.

Now the problem is accessing the installation to control it.

I've created a new user, to test and it keeps freezing everytime I enter. Any thoughts?

Attachments
Reply
IC_Systems
Captain IC_Systems
Captain

Posted: ‎2024-12-21 10:40 PM

0 Likes
0
911
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-21 10:40 PM

@tiago_oesteprisma This could be a network issue, try to connect directly to the controller and see if it is resolved!

Best Regards,
Reply
tiago_oesteprisma
Crewman tiago_oesteprisma
Crewman

Posted: ‎2024-12-26 08:57 AM

0 Likes
0
844
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-26 08:57 AM

Thanks! It's very strange. We've several controllers working, and only this have this issue. You can close this topic. I'll open a new one regardind this if necessary.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of