KNX/DALI gateway - Philips Xtanium

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • KNX/DALI gateway - Philips Xtanium
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Related Products
product field
SpaceLogic KNX - 4ʺ Touch Unit
product field
KNX Push Button Dynamic Labeling, universal
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SpaceLogic KNX Forum
Start a Topic
sesa174915
sesa174915 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2015-01-28 01:00 AM . Last Modified: ‎2024-07-15 12:03 AM

1 Like
5
1070
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-01-28 01:00 AM

KNX/DALI gateway - Philips Xtanium

We have some issues with the KNX/DALI gw MTN6725-0001 firmware 1.2.0 in combination with Philips Xtanium LED panels. Control works fine for a while (sometimes weeks) but then dimming stops working. Also we can no longer connect via ETS plug-in to the DALI gw. When we reload the application or cut the power, everything works fine again. Any suggestions ? Does anyone have experience with a DALI analyser ? In attachment you can find the datasheet for the LED panel.

  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
    KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (3)
Attachments
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
esteve_budia
Lieutenant esteve_budia Lieutenant
Lieutenant

Posted: ‎2015-01-28 01:00 PM

0 Likes
0
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-01-28 01:00 PM

Reply
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2015-02-04 02:36 AM

0 Likes
3
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-02-04 02:36 AM

Hello Hannes

We had some problems with Philips Xitanium ballasts in the past. These problems were related to addressing the LED drivers. Once they received a DALI short address it was not possible to modify this address. Philips is expecting a special procedure for doing this (which BTW is not according to DALI standard).

Nevertheless we modified the firmware of the KNX DALI Gateway and this is now supported. This installation contains several thousand of these Philips Xitanium LED drivers (but is different type that used in your project). The installation is working properly now for several months.

Two times we saw thermal problems of ballasts (from different manufacturers) that were mounted in a false ceiling without ventilation. Ballasts could not be controlled. Only after reset of the ballasts the installation worked again.

Are you resetting the KNX DALI Gateway only? Or do you have as well to reset the ballasts? You mentioned that after download of the application everything works fine. I wonder that before you couldn't communicate with ETS but it seems you are able to download the application. Do I understand correctly that only donwnload of application (without resetting KNX DALI Gateway or LED drivers) makes it work again?

BR, Heribert

Reply
sesa174915
sesa174915 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2015-02-04 04:41 AM

0 Likes
2
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-02-04 04:41 AM

Hello Heribert,

The integrator suspects that when he did the application download, the installer powered down/up the DALI gateway before he arrived.

So, sometimes only powering down/up the DALI gateway solves the problem. Other times you also need to download the application.

The ballasts remain powered. By resetting the DALI ballasts you mean cutting the power to the ballasts ?

Downloading the application works but when we open the plug-in we can't connect to the DALI gateway.

It has been weeks since the last problem, but this was the case the last time aswell.

Kind regards,

Hannes

Reply
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2015-02-04 08:06 AM

0 Likes
0
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-02-04 08:06 AM

Hello Hannes

I would propose to check the following.

When the error occurs

- is there the possibility to control the lamps by the use of the buttons on the device
- is it possible to connect to the DALI Gateway via IP connection (web interface) and control the lamps
- is the display reacting on commands initiated by the buttons on the device?

This of this is to find out if there is still communication from the device to the DALI line but no communication from KNX bus.

Some more questions:

When was the firmware update done?

Are you sure that you are using firmware 1.2.0? It was released in November last year. As you mention the installation works well for weeks I guess the update was done not that long ago. Please doublecheck if really the latest firmware is on the device. Version number is indicated on the display.

Do you know how old the devices are?

Are the DALI gateways integrated in an IP network?

Best regards
Heribert

Reply
Heribert_Dölger
Commander Heribert_Dölger Commander
Commander

Posted: ‎2015-02-05 03:53 AM

0 Likes
0
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-02-05 03:53 AM

Hello Hannes

some more ideas what could cause your problem:

The DALI Gateway has several modes that cause that the lamps can no longer be controlled:
- panic mode
- test of emergency lamps
- burn-in of new lamps

Please check if one if these modes is active when you see the problem that lamps can no longer be controlled.

BR
Heribert

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore