Hello,
I have heating actuator MTN6730-0001, and I want to disable the actuator in the summer.
I try to use the summer/winter change-over object, but it didn't react as expected (maybe I missed something)
what I want to achieve:
when trigger this object it should close all valves and disable any external valve commands.
I tried to use this object because its value saved in the memory and will be restored after power fail
So does it possible to achieve this function via this summer/winter object or should I use another object, but I prefer to be immune against power fail.
Link copied. Please paste this link to share this article on your social media post.
Hello IC-Systems,
sorry for the late reply!
The Summer/Winter-Mode is not exactly what you are looking for as it changes only setpoints for the valve output for emergency operation or forced position.
I would propose to work with the function "forced positon".
The forced position function you can activate with a dedicated object also, you can defind a certain valve value and you can define the behaivour for a power failure/ETS-Download.
With the summer/winter function you can even influence this forced values.
Meaning if you have a forced value of 0% .... this can be a good value during the summer monthes ... but maybe a big mistake within the wintertime. So for the wintertime you could set 10% in order not to coole down the room fully.
So please have a deeper look on the function "forced position". And if needed on the function "Summer/Winter".
Link to the System-User-Guide
Link copied. Please paste this link to share this article on your social media post.
Hello community,
I try the 2bit service mode object but its value lost after power fail and valves could work.
any updates about the summer/winter changeover object and how to use it properly?
BR,
Link copied. Please paste this link to share this article on your social media post.
Hello IC-Systems,
sorry for the late reply!
The Summer/Winter-Mode is not exactly what you are looking for as it changes only setpoints for the valve output for emergency operation or forced position.
I would propose to work with the function "forced positon".
The forced position function you can activate with a dedicated object also, you can defind a certain valve value and you can define the behaivour for a power failure/ETS-Download.
With the summer/winter function you can even influence this forced values.
Meaning if you have a forced value of 0% .... this can be a good value during the summer monthes ... but maybe a big mistake within the wintertime. So for the wintertime you could set 10% in order not to coole down the room fully.
So please have a deeper look on the function "forced position". And if needed on the function "Summer/Winter".
Link to the System-User-Guide