Hello,
When you import an esf file with the names of objects in Russian, we get the squares in place of object names in the HL (see attached file).
Is there a way to solve this problem without renaming all the objects manually?
Kind regards,
Aleksandr,
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi,
keep in mind firstly set correct character settings to Cyrilic -> Windows-1251
after that you can make Encoding >> Convert to UTF-8
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi,
can you attach example of the esf file?
BR
Tomas
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Alexander,
here I attach a file, which you can restore and it works fine.
The problem of your file is encoding ( it is encoded in type 1251).
You can open the file in Notepad++ and select Encoding >> Convert to UTF-8.
Then save the file and you can use it in homeLYnk.
I do not know, when is the original encoding of the esf file coming from, but is most probably derived from language settings of your Windows PC or ETS.
Best Regards
Tomas
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Alex,
can you mark this topic as Answered? 🙂
Thanks
Tomas
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Thanks, Peter.
It's work fine!
Best regards,