DALI ECG Power Recovery Problem

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • DALI ECG Power Recovery Problem
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
121
Erwin-vd-Zwart
Sisko Erwin-vd-Zwart Sisko
54
Heribert_Dölger
Lt. Commander Heribert_Dölger Lt. Commander
30
FZetina
Lt. Commander FZetina Lt. Commander
27
View All
Related Products
product field
SpaceLogic KNX - 4ʺ Touch Unit
product field
KNX Push Button Dynamic Labeling, universal
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Solved
joseloureiro
Crewman joseloureiro
Crewman

Posted: ‎2023-07-19 06:29 AM . Last Modified: ‎2024-07-14 11:42 PM

0 Likes
3
1111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-19 06:29 AM

DALI ECG Power Recovery Problem

Hi,

 

I'm having a problem with the ECG power recovery function on a MTN6725-0004 DALI Gateway. In our site the DALI Gateways are powered by an UPS. I selected the option Last Value for ECG power recovery but it just isnt working that way. If I have all the lights turned on, when I trip the ECG breakers and turn it back on, some of the lights turn back on, others not. If I do the other way around and turn off all the lights before I trip the breakers, same thing happens, I turn it back on, some of the lights turn on, others not. This is very weird because the behaviour is the same.

 

I'm not sure if this might be related with the type of ECG installed in this section of the building as in other areas of the building the ECGs assume the last value on ECG power recovery. Both areas have the following settings:

 

1.png

 

2.png

 

Any idea of what might be happening?

  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
    KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (3)
Labels
  • Labels:
  • Scripts
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Heribert_Dölger
Lt. Commander Heribert_Dölger Lt. Commander
Lt. Commander

Posted: ‎2023-07-20 01:25 AM

0 Likes
0
1105
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-20 01:25 AM

Hello

 

Some background information why you see this behaviour:

The DALI gateway permanently monitors the status of all ECGs. Depending on the number of connected ECGs this process can take up to 2 min to check all ECGs.

Example: During a 45sec power cut in your installation the DALI gateway will have detected some of the connected ECGs as no longer present but not yet the others. If an ECG is detected as present again the DALI gateway will send its last value to the ECG. But this will only happen for the ECGs that before were detected as "missing". Not for the others. This is why you see "strange" behaviour that after power return some ECGs are on and others are off.

See Answer In Context

Reply
Replies 3
Heribert_Dölger
Lt. Commander Heribert_Dölger Lt. Commander
Lt. Commander

Posted: ‎2023-07-20 01:25 AM

0 Likes
0
1106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-20 01:25 AM

Hello

 

Some background information why you see this behaviour:

The DALI gateway permanently monitors the status of all ECGs. Depending on the number of connected ECGs this process can take up to 2 min to check all ECGs.

Example: During a 45sec power cut in your installation the DALI gateway will have detected some of the connected ECGs as no longer present but not yet the others. If an ECG is detected as present again the DALI gateway will send its last value to the ECG. But this will only happen for the ECGs that before were detected as "missing". Not for the others. This is why you see "strange" behaviour that after power return some ECGs are on and others are off.

Reply
joseloureiro
Crewman joseloureiro
Crewman

Posted: ‎2023-07-20 06:15 AM

0 Likes
1
1100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-20 06:15 AM

Hi,

 

Thank you for your reply.

 

I'm a bit confused. I saw the post titled "Powering DALI gateway" and the problem is indeed similar. But from my understanding if I use the setting last value, even if the ECG power cut is less then 2 minutes it shouldn't really matter, right?

 

Regarding the ECGs that the DALI gateway detects as not present, once they power up again the gateway will tell them they should assume the last value before the power cut.

 

While the ECGs that the Gateway thinks are still present shouldn't change value at all. When power comes back they should also assume the value they had before the power cut, right? Or do they need the gateway to resend the value?

Reply
Heribert_Dölger
Lt. Commander Heribert_Dölger Lt. Commander
Lt. Commander

Posted: ‎2023-07-21 02:53 AM . Last Modified: ‎2023-07-21 02:55 AM

0 Likes
0
1098
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-21 02:53 AM

Hello again

 

Your expectation indeed is correct: after power recovery the ECG should go to the configured value. The ETS parameter that you can set in the DALI gateway configuration is written into the ECG and the ECG has to adopt this value after power recovery.

 

As it is not the case in your installation it seems either the ECG is not supporting it or the value was not properly written into the ECG during DALI Download process. According DALI specification the ECG must support this feature. In the initial DALI specification only fixed values were specified ("last value" was not possible). But the DALI specification had been changed about 10 years ago and the feature "last value" is part of the DALI specs since then and every ECG has to support it. If the ECG doesn't support this you should contact the manufacturer of the ECGs.

 

If the value has not been properly written into the ECG you might try to repeat "download to DALI" in the DCA. But you will need to do a modification in the settings otherwise the gateway won't write the values to the ECGs.

 

The behaviour at power recovery has to be managed by the ECG. The DALI gateway doesn't "know" about the mains power failure of the ECGs until the monitor process has been finalised for the whole DALI line (the mentioned 2 minutes). Due to that the gateway will only re-write the last value if it has detected the ECG as "missing".

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of