Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Actuator to control blinds and cooling heating

SpaceLogic KNX Forum

Schneider Electric SpaceLogic KNX forum to get support and share knowledge including selection, installation and troubleshooting for spaceLYnk, Wiser for KNX, eConfigure KNX, SpaceLogic KNX Hybrid module and other topics.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic KNX Forum
  • Actuator to control blinds and cooling heating
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Thomas_Rohde
Sisko Thomas_Rohde Sisko
132
Erwin-vd-Zwart
Janeway Erwin-vd-Zwart Janeway
60
Heribert_Dölger
Commander Heribert_Dölger Commander
31
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Related Products
product field
SpaceLogic KNX - 4ʺ Touch Unit
product field
KNX Push Button Dynamic Labeling, universal
product field
Wiser for KNX : logic controller

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic KNX Forum
Start a Topic
Solved
PiotrJakubczyk
Sisko PiotrJakubczyk Sisko
Sisko

Posted: ‎2023-01-17 06:56 AM . Last Modified: ‎2024-07-14 11:43 PM

0 Likes
3
915
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-17 06:56 AM

Actuator to control blinds and cooling heating

Hello 

 

We are migrating old system (LON based) to new system and device must control heating, cooling and blinds. I wonder if 

MTN6705-0008 would be appropriate for this task or i should use other actuator, or maybe it is impossible in KNX and i should use 2 actuators?  (one to control light and blinds and second as valve driver)

 

 

 Schemtaic KNX control.jpg

 

MTN6214-0460 as RCU and MTN6705-0008 as actuator

  • Thumbnail of SpaceLogic KNX - 4ʺ Touch Unit
    SpaceLogic KNX - 4ʺ Touch Unit
  • Thumbnail of KNX Push Button Dynamic Labeling, universal
    KNX Push Button Dynamic Labeling, universal
  • Thumbnail of Wiser for KNX : logic controller
    Wiser for KNX : logic controller
View products (3)
Labels
  • Labels:
  • Local App
  • Protocols
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2023-01-18 12:17 AM

1 Like
0
910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-18 12:17 AM

Hi Piotr,

to "MTN6705-0008 would be appropriate for this task or i should use other actuator, or maybe it is impossible in KNX and i should use 2 actuators?  (one to control light and blinds and second as valve driver)"

You are already on the right track. MTN6705-0008 is not the correct device to deal with the valve drives.
I would propose to use two specialist. MTN6705-0008 for Switch/Blid Tasks and MTN6730-0002 SpaceLogic KNX Valve Drive Controller for the heating and cooling tasks.
With this you can even select if you want to use 24V Valvedrives or directly 230V.
And it has the advantage that it has 6 RTCs already on board.
So that you can use pushbuttons which just have a temperature sensor instead of a dedicated RTC like the Pushbutton Pro T.

2023-01-18_08h58_56.png

Link to the Valve Drive Controller 

Kind regards
Thomas

Application Design Engineer

See Answer In Context

Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2023-01-19 02:34 AM

1 Like
0
894
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-19 02:34 AM

It will work as you described. But there are two topics which you should have in mind:

1. As in your first picture you selected 24V valvedrives. Please supply them with 24V AC and NOT DC as it is not allowed to switch DC-Loads with MTN6705-0008.
2. Keep in mind the Switching-Cycles of MTN6705-0008 as depending on the setup of the RTC it will often be switched.

2023-01-19_11h21_34.png

 

Kind regards
Thomas

Application Design Engineer

See Answer In Context

Reply
Replies 3
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2023-01-18 12:17 AM

1 Like
0
911
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-18 12:17 AM

Hi Piotr,

to "MTN6705-0008 would be appropriate for this task or i should use other actuator, or maybe it is impossible in KNX and i should use 2 actuators?  (one to control light and blinds and second as valve driver)"

You are already on the right track. MTN6705-0008 is not the correct device to deal with the valve drives.
I would propose to use two specialist. MTN6705-0008 for Switch/Blid Tasks and MTN6730-0002 SpaceLogic KNX Valve Drive Controller for the heating and cooling tasks.
With this you can even select if you want to use 24V Valvedrives or directly 230V.
And it has the advantage that it has 6 RTCs already on board.
So that you can use pushbuttons which just have a temperature sensor instead of a dedicated RTC like the Pushbutton Pro T.

2023-01-18_08h58_56.png

Link to the Valve Drive Controller 

Kind regards
Thomas

Application Design Engineer
Reply
PiotrJakubczyk
Sisko PiotrJakubczyk Sisko
Sisko

Posted: ‎2023-01-18 04:44 AM

0 Likes
0
903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-18 04:44 AM

Unfortunately we have to adopt existing control box. There is no place for 2 module... We planning to use 2-step control (switching) in MTN6214-0460 and use "Correcting variable heating" to create control group with MTN6705-0008 Master Output 1 (switch). In principle this should be possible to create? 

Group adress.jpg

 

Reply
Thomas_Rohde
Sisko Thomas_Rohde Sisko
Sisko

Posted: ‎2023-01-19 02:34 AM

1 Like
0
895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-19 02:34 AM

It will work as you described. But there are two topics which you should have in mind:

1. As in your first picture you selected 24V valvedrives. Please supply them with 24V AC and NOT DC as it is not allowed to switch DC-Loads with MTN6705-0008.
2. Keep in mind the Switching-Cycles of MTN6705-0008 as depending on the setup of the RTC it will often be switched.

2023-01-19_11h21_34.png

 

Kind regards
Thomas

Application Design Engineer
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore