APL ERROR IN MTN6212-03XX
Hi colleagues,
I have a problem with a mtn6212-03. On screen it shows "APL" and I'm not able to download application via ETS5.7.4 on it? I tested all .KNXPROD and .VD files on it, but they didn't work. Is there the same problem for others? Does it have a solution?
Link copied. Please paste this link to share this article on your social media post.
2025-01-1609:19 AM
Hello NAEIM,
"APL" on the display indicates that a previous loaded application program has been unloaded from the device, as also shown in the ETS download history. Have you tried to use a different Bus interface?
I honestly don't remember if those devices need a plugin or not. Maybe you can try to enable the "compatibility" mode in the general settings of ETS and then try to download the application program again.