PulseCBusLevel

SpaceLogic C-Bus Forum

Schneider Electric forum about the C-Bus platform to get support and share knowledge including Network Automation Controller (NAC), Application Controller (AC) at selection, installation and troubleshooting sides.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic C-Bus Forum
  • PulseCBusLevel
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sesa96364
sesa96364 Schneider Alumni (Retired)
9
KCWong
Lieutenant KCWong Lieutenant
4
ZeeZee97
Administrator ZeeZee97 Administrator
1
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SpaceLogic C-Bus Forum
Start a Topic
Solved
Titsonabull
Crewman Titsonabull
Crewman

Posted: ‎2023-12-06 10:18 AM

1 Like
5
1544
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-06 10:18 AM

PulseCBusLevel

Hi I've installed C-Bus Firmware for LSS5500SHAC Automation Controller V1.15.0 (V1.15.0) and since then all my PulseCBusLevel commands are giving multiple triggers and seem to be turning off groups before turning them back on. 

 

Any advice

 

 

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MarkHenry
Lieutenant | EcoXpert Master MarkHenry Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2023-12-08 11:12 PM

1 Like
1
1503
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-08 11:12 PM

Haven't seen multiple commands but the issue still exists where the expiry function is not cancelled when a command has been sent during the expiry time.

e.g.

Send Pulse Group1 to 255 and after 20 sec set to 0

During the 20 sec expiry time send a command to Group1 to any level, for this example say 50%

Group1 turns off 20sec after the initial command.

 

Expect that the expiry timer would be cancelled when a command is received without a pulse as it did previously in any PICED devices. Have not used pulse in NAC at all due to this.

See Answer In Context

Reply
Replies 5
DarrenMullighan
Ensign DarrenMullighan Ensign
Ensign

Posted: ‎2023-12-07 08:32 PM

0 Likes
1
1533
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-07 08:32 PM

Hi there, the 1.15.0 firmware addressed some issues around the PulseCBusLevel command. Funnily enough to actually prevent the issuing of multiple commands. Out of interest, what firmware did you upgrade from? and does this affect any new scripts which use this function? Regards, Darren
Reply
Titsonabull
Crewman Titsonabull
Crewman

Posted: ‎2023-12-08 06:58 AM

0 Likes
0
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-08 06:58 AM

Hi Darren. Thank you for your reply.

I’ve updated from V1.6 I think and updated to V1.15.

I had several simple event  based scripts to pulse groups on and return them to off after a period of time. The script was activated by a group on a schedule. This group was also turned on by a toggle switch on a visualization page. This allowed the script to run when the toggle switch was turned on or the schedule ran.  Within the script the group for the activation of the script was also pulsed for the same time length.

By turning off the toggle switch it used to cancel the pulse command and off each group that was being pulsed including the toggle switch that activated the script. This allowed me to see on the visualization page if the  groups being pulsed where on or off. Code shown below

 

if (GetCBusLevel(0, 49, 4) >= 1)  -- toggle switch for activation of script which is also activated from             schedule

 then

 PulseCBusLevel(0, 56, 43, 255, 0, 5, 0) -- Light to be pulsed on for 5 seconds and then turned off

PulseCBusLevel(0, 49, 4, 255, 0, 5, 0) 

 end

 

 

With the new firmware when I toggle the switch it pules the groups on and off in a loop. It’s like the pulse command is being reactivated by the pulse command of the group being pulsed within the script and turning off the toggle switch does not cancel the pulse command.

 

Any help would be much appreciated. Regards, Colin

Reply
Mr_C
Ensign Mr_C Ensign
Ensign

Posted: ‎2023-12-08 09:28 PM

0 Likes
0
1508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-08 09:28 PM

Hi  

1.15.0  Release notes  statements 
Fixed an issue related to the PulseCBusLevel() function, which appeared to send multiple first
stage commands.
• Fixed an issue related to the "Execute during ramping" option for an Event-based script, which
was not functioning.

Out of interest does the event script action the group that creates the event,   if so , Please check to make sure your Execute during ramping is not set. 

An issue with PulseCBusLevel was fixed in 1.15.0  but t might be the execute when ramping fix could possible causing the difference you currently see. 

Schneider Electric Australia PTY
Reply
MarkHenry
Lieutenant | EcoXpert Master MarkHenry Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2023-12-08 11:12 PM

1 Like
1
1504
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-08 11:12 PM

Haven't seen multiple commands but the issue still exists where the expiry function is not cancelled when a command has been sent during the expiry time.

e.g.

Send Pulse Group1 to 255 and after 20 sec set to 0

During the 20 sec expiry time send a command to Group1 to any level, for this example say 50%

Group1 turns off 20sec after the initial command.

 

Expect that the expiry timer would be cancelled when a command is received without a pulse as it did previously in any PICED devices. Have not used pulse in NAC at all due to this.

Reply
Titsonabull
Crewman Titsonabull
Crewman

Posted: ‎2023-12-12 05:53 AM

0 Likes
0
1433
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-12 05:53 AM

Hi All, 

thanks for the reply's. Got it working all be it over a couple of event scripts. Not sure how it worked previously but with the new upgrade it works differently and requires a bit more thought going into the scripting when using the pulse command as pulse is no longer canceled with the deactivation of the pule trigger. Learned a lot while trying to figure it out and really appreciate those who took the time to reply. 

Regards 

Colin

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore