Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric forum about the C-Bus platform to get support and share knowledge including Network Automation Controller (NAC), Application Controller (AC) at selection, installation and troubleshooting sides.
Search in
Link copied. Please paste this link to share this article on your social media post.
Hi,
'PCI Failed to reset. Unable to open the network'
That error window message coming when I'm trying to open a Cbus Network using CBus Toolkit. I'm using LSS5500SHAC as the gateway to Cbus network.
Cbus Toolkit v1.15.6.
SHAC firmware v1.6
Hardware v1.0
Please help to find solution for this issue.
Salam,
Bayu
Posted: 2020-01-08 09:38 AM . Last Modified: 2025-08-12 05:15 AM
Link copied. Please paste this link to share this article on your social media post.
Hi
the community members can you help this member on this topic please?
@Coppo do you think you can advise on this topic?
@Bayu , in the meantime, please check the Knowledge base, maybe you can find useful information.
But if you still in the same situation please do not hesitate to inform us here.
Have a nice day.
Link copied. Please paste this link to share this article on your social media post.
Hi, your best information source would be via Aitor Martinez or CBus Level 3 Tech support - Steve Dunn (adelaide - Gepps Cross).
some possible things to look into are:
1) You did not install the 5500 NAC/SHAC USB drivers when installing tool kit....re-install toolkit
2) You have not changed the 2 x unit addresses in the NAC/SHAC off 255.
The NAC/SHAC has 2 internal CBus interfaces, 1 x PCU (USB) + 1 x CNI (ethernet), even though you have 1 actual product, these 2 interfaces aqre seen as seperate things in the Toolkit database and will require unique unit address on each.
This will also affect if you are trying to do a network 'UNRAVEL" where you have multiple new units still no 255 unit address, you need to manually change the 2 x unit address on the NAC/SHAC first , before you can use the un-ravel function otherwise you will get an error message.