LSS5500NAC wont lock NTP status

SpaceLogic C-Bus Forum

Schneider Electric forum about the C-Bus platform to get support and share knowledge including Network Automation Controller (NAC), Application Controller (AC) at selection, installation and troubleshooting sides.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic C-Bus Forum
  • LSS5500NAC wont lock NTP status
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sesa96364
sesa96364 Schneider Alumni (Retired)
9
KCWong
Lieutenant KCWong Lieutenant
4
ZeeZee97
Administrator ZeeZee97 Administrator
1
View All

Recommended Forums

  • Intelligent Devices Forum

  • SmartConnector Forum

  • Metering & Power Quality

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SpaceLogic C-Bus Forum
Start a Topic
Craig_DnA
Ensign Craig_DnA
Ensign

Posted: ‎2024-06-28 08:27 PM

1 Like
2
897
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-28 08:27 PM

LSS5500NAC wont lock NTP status

Hello SpaceLogic Community. Just seeing if anyone can help me with this one. I have installed a LSS5500NAC and made a schedule which was running fine for a month. Then for some reason the clock went way out of sync and I noticed the NAC's NTP was not locked. I synced the time from my computer with it, which will work for a couple of hours, then it will go way out of sync again. The clock synchronization is enabled in the NTP settings and has all the servers 1 to 4 filled in but it wont seem to lock? I have taken some screen shots remotely and I can ping google from the NAC's network utilitie so it's definitely connected to the internet but I can't ping the NTP server. I also tried 

0.au.pool.ntp.org

and I get the bad address error also.

I'm running Version 1.17.0 firmwear. Any sugestions???

 

Ping NTP.png   

Google Ping.png

 

NTP Status.png

 

 

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
Mr_C
Ensign Mr_C Ensign
Ensign

Posted: ‎2024-07-09 01:59 AM

3 Likes
1
824
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-09 01:59 AM

Hi Craig 

I can reproduce your issue,  but only if my controller is configured with DHCP for the network interface,  When configured in this way i am unable to get any response to ping events from the controllers tools that include a URL, so the URL for NTP would appear not to be resolving. hence not locked. 

We are investigating the issue to ID root cause. 

However for now a possible work around,
if you wish to use DHCP  for IP assignment,  then please try with the DNS 1 and DNS 2 fields left blank and save.   these changes,  on reboot check the URL is resolving using PING tools on the controller. 

If that does not work,  I had success by assigning a Static IP address and all settings to the controller,  I used the stock standard DNS1 = 8.8.8.8 and DNS 2 = 8.8.4.4   Save and apply the address and then again attempt the Ping for the URL,   

We will comment further when identifying the root cause, as to why the DNS services did not resolve the URL

Schneider Electric Australia PTY
Reply
Craig_DnA
Ensign Craig_DnA
Ensign

Posted: ‎2024-07-30 04:16 AM

0 Likes
0
764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-30 04:16 AM

Thanks mate, 

Sorry for the slow reply, been overseas.

 

Just before I left I managed to get the NTP status to lock. The sites network is managed with a UniFi Dream Machine Pro router and I noticed on the Ubiquiti Community that other were also having NTP problems on their network when they used a URL for the NTP. I have changed Server 1 to 131.188.3.221 and the clock locked straight away.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore