How can I interface a C-bus network with BACnet?
SpaceLogic C-Bus Forum
Schneider Electric forum about the C-Bus platform to get support and share knowledge including Network Automation Controller (NAC), Application Controller (AC) at selection, installation and troubleshooting sides.
  • EcoStruxure Building
  • Light and Room Control
  • SpaceLogic C-Bus Forum
  • How can I interface a C-bus network with BACnet?
sesa96364
sesa96364 Schneider Alumni (Retired)
9
KCWong
Lieutenant KCWong Lieutenant
4
ZeeZee97
Administrator ZeeZee97 Administrator
1
Back to SpaceLogic C-Bus Forum
sesa8875
sesa8875 Schneider Alumni (Retired)
Posted: ‎2014-04-08 11:31 PM
1235
What are the limitations? What is the most cost optimised solution? Which devices are required?
Posted: ‎2014-04-16 08:56 PM
You can use our Cbus Bacnet gateway. At the moment, only support 1 application and max 255 addresses.
Coppo
Lt. Commander Coppo Lt. Commander
Lt. Commander
Posted: ‎2019-03-20 10:48 PM
5500NAC  Network automation controller.
 or
LSS5500NAC ( Schneider Branded )
5 module wide DIN mount
BACnet IP server onboard
supports 500 BACnet points
Read/Write for BACnet points to /from a BACnet IP Client (BMS)
BACnet IP only,  does not support BACnet ETHERNET protocol.
1 X RJ45 connection