VFD WIRING HELP

Solutions for Motor Management

Get support to configure, troubleshoot, update or upgrade your motor management solution built with Altivar variable speed drives and Tesys devices to start, control, protect and monitor Low Voltage and Medium Voltage motors and loads, covering direct start, soft start and variable speed control.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Solutions for Motor Management
  • VFD WIRING HELP
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BJacqz
Commander BJacqz Commander
48
LeoLazzaro
Lieutenant LeoLazzaro Lieutenant
16
PriscilaCunha22
Lieutenant JG PriscilaCunha22 Lieutenant JG
12
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
10
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Solutions for Motor Management
Solved
kishore1march
Lieutenant JG kishore1march
Lieutenant JG

Posted: ‎2022-06-01 02:50 AM

0 Likes
2
2304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-01 02:50 AM

VFD WIRING HELP

Dear,

 

SITE CONDITION - I have a panel with a VFD 90KW and a same capacity of soft starter, where a 75 sqmm cable is being connected to L1,L2,L3 terminals of VFD and another three cables of same size is being looped from VFD input terminals to soft starter input terminals(L1,L2,L3). Now the VFD and Soft starter L1,L2,L3 are looped without any individual MCCB and VFD L1,L2,L3 have two 75sqmm cable connected in each terminal.

 

QUERY -

1. if the Soft starter L1,L2,L3 got short circuit internally, will it affect the VFD's L1,L2,L3?

2. the rated tightening torque for VFD will differ if 2 cables are terminated in each terminals (L1,L2,L3)?


Pls suggest any problems in the present wiring and any good practice to be followed.

 

Rough sketch of wiring is attached.

Attachments
Labels
  • Labels:
  • Design & Build
  • Selection & sizing
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Werner_JUPPA
Crewman Werner_JUPPA Crewman
Crewman

Posted: ‎2022-06-02 10:20 PM

1 Like
1
2269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-02 10:20 PM

 

Hello

 

These two devices probably never run at the same time, otherwise a common supply of 75mm² would be too small.

 

1. As soon as the Softstarter fails, the MCCB will trip and the VFD has no power supply anymore (and vice-versa).

2, Two wires of 75mm² each will probably fit in these terminals, but they are not designed for that. The terminals are designed for one wire with a maximum cross section of 120mm².

 

Basically, we would not recommend this wiring.

Either the two devices are powered individually by two MCCBs, or the two devices are protected locally with two circuit breakers (see attached drawing). These should be dimensioned in such a way that, in the event of a fault, the local CB switches off and not the MCCB. Both architectures are therefore redundant and the VFD remains in operation if the Softstarter should fail.

 

See Answer In Context

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Werner_JUPPA
Crewman Werner_JUPPA Crewman
Crewman

Posted: ‎2022-06-02 10:20 PM

1 Like
1
2270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-02 10:20 PM

 

Hello

 

These two devices probably never run at the same time, otherwise a common supply of 75mm² would be too small.

 

1. As soon as the Softstarter fails, the MCCB will trip and the VFD has no power supply anymore (and vice-versa).

2, Two wires of 75mm² each will probably fit in these terminals, but they are not designed for that. The terminals are designed for one wire with a maximum cross section of 120mm².

 

Basically, we would not recommend this wiring.

Either the two devices are powered individually by two MCCBs, or the two devices are protected locally with two circuit breakers (see attached drawing). These should be dimensioned in such a way that, in the event of a fault, the local CB switches off and not the MCCB. Both architectures are therefore redundant and the VFD remains in operation if the Softstarter should fail.

 

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

kishore1march
Lieutenant JG kishore1march
Lieutenant JG

Posted: ‎2022-06-06 09:24 PM

In response to Werner_JUPPA
0 Likes
0
2227
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-06 09:24 PM

Dear Werner,

 

This is a well guided answer. Thanks for your info and time. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of