Is a mirror contact the same as a positively driven contact?

Solutions for Motor Management

Get support to configure, troubleshoot, update or upgrade your motor management solution built with Altivar variable speed drives and Tesys devices to start, control, protect and monitor Low Voltage and Medium Voltage motors and loads, covering direct start, soft start and variable speed control.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Solutions for Motor Management
  • Is a mirror contact the same as a positively driven contact?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BJacqz
Commander BJacqz Commander
48
LeoLazzaro
Lieutenant LeoLazzaro Lieutenant
16
PriscilaCunha22
Lieutenant JG PriscilaCunha22 Lieutenant JG
12
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
9
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Solutions for Motor Management
Solved
Gingko_Elec
Lieutenant JG Gingko_Elec
Lieutenant JG

Posted: ‎2021-03-25 08:21 AM

2 Likes
2
8254
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-25 08:21 AM

Is a mirror contact the same as a positively driven contact?

Hello,

For a safety chain on a conveyor belt line, it’s requested to have mirror contacts attached to the

Contactor that switch On and OFF the belt. Is a mirror contact the same as a positively driven contact?

Thanks for your answer

Labels
  • Labels:
  • Design & Build
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TeSysMen
Ensign TeSysMen Ensign
Ensign

Posted: ‎2021-03-29 08:18 AM

3 Likes
0
8212
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-29 08:18 AM

the term "positively driven contact" is used in IEC 60947-5-1 to define a mechanicaly interlock: combination of NO/NC contacts for control relays. it prevents contact to be closed/opened in case the opposite contact is welded.

 

the IEC 60947-4-1 standard defines the term "mirror contact" for power contactors and concerns only NC auxilliary contact that will guarantee that it cannot be closed simultaneously with an NO main power contact.

in your case you are looking for mirror contact.

 

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
TeSysMen
Ensign TeSysMen Ensign
Ensign

Posted: ‎2021-03-29 08:18 AM

3 Likes
0
8213
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-29 08:18 AM

the term "positively driven contact" is used in IEC 60947-5-1 to define a mechanicaly interlock: combination of NO/NC contacts for control relays. it prevents contact to be closed/opened in case the opposite contact is welded.

 

the IEC 60947-4-1 standard defines the term "mirror contact" for power contactors and concerns only NC auxilliary contact that will guarantee that it cannot be closed simultaneously with an NO main power contact.

in your case you are looking for mirror contact.

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-04-06 01:22 AM

4 Likes
0
8173
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-06 01:22 AM

I think the confusion comes sometimes from the translation.

If we speak about the aux. contacts of Contactors (NO or NO) we speak first of all about " linked contacts" meaning probably the same as positive driven. As explained by the others the mirror contact is specifically referring to the NC contact to be used in safety circuits. :

In a TeSys D contactor that has a NO and a NC aux contact both contacts are not closed at the same time and the NC contact and the main poles are not open at the same time. They are ' linked '  to the main poles.

Take care some of our competitors don't offer these linked contacts not in there design. They often want to speak about " safety contactors"  which is a none existing term in the machine directive or the EN60294. What they mean is that they have mechanically fixed the separate aux. contacts so they cann't be removed. For customers that like the approach of a " safety contactor "  we still have the red covers which makes it a visual part of a safety chain. Our contactors offer maximum safety from its design. There is a TVDE/TuV certificate to proof it.

 

Customers are often using the term " mechanical forced contacts " when they mean linked contacts. An aux contact of a contactor is never forced. Forced contacts can be recognized by an horizontal arrow in a circle. Examples of forced contacts are pushbutton contacts and limit switches. They are  forced open either by your finger or by an object in case of a limit-switch.

Of course these components are also part of a safety chain

Schneider is the supplier when it comes on safety solutions :

- Safety Control with e-stops and pull wire switches

- Safety Detections with limit-switches, coded switches, key-switches, light curtains

- Safety Monitoring with safety-relays, safety-controllers and safety plc.

- Safety in installation stop by Freq. converters with or without DC breaking, Circuit-breakers, Contactors, Vario type switches.

- Safety Visualisation with all the Signalling components from pilot lights to beacons, flashing lights and sirens.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now