FDR won't fire LO1 on TeSys T in Local

Solutions for Motor Management

Get support to configure, troubleshoot, update or upgrade your motor management solution built with Altivar variable speed drives and Tesys devices to start, control, protect and monitor Low Voltage and Medium Voltage motors and loads, covering direct start, soft start and variable speed control.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Solutions for Motor Management
  • FDR won't fire LO1 on TeSys T in Local
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BJacqz
Commander BJacqz Commander
49
LeoLazzaro
Lieutenant LeoLazzaro Lieutenant
16
PriscilaCunha22
Lieutenant JG PriscilaCunha22 Lieutenant JG
15
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Solutions for Motor Management
Start a Topic
Solved
TMS
TMS
Cadet

Posted: ‎2023-04-21 10:26 AM

0 Likes
2
1407
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-21 10:26 AM

FDR won't fire LO1 on TeSys T in Local

I have a TeSys T.  I have an FDR attached to it.  IO6 is wired ON for L/R control.

I have SoMove connected to the LTMR simultaneously.

In SoMove IO6 status is ON.

I can change between L/R with the FDR.  In the upper RT corner the FDR says "RDY"

With the FDR in Local, pressing either RUN button does nothing.

In Remote, writing to the 704 bit for Run Forward (0) turns on the LO1.

 

Why doesn't this work with the FDR?  FDR is set to HMI not Terminals for Local control

Labels
  • Labels:
  • Drives & Motor Control
  • Soft Starters
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Bruno_Hussenet
Crewman Bruno_Hussenet Crewman
Crewman

Posted: ‎2023-05-05 05:29 AM

1 Like
0
1372
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-05 05:29 AM

Hello TMS,
Sorry for the time taken in responding to your request.
My setup : LTMR08EBD V2.9 + LTMCUF (FDR)
With the following settings in SoMove, Input I6 is wired ON  ,  I can change between L/R with the FDR (LTMCUF).  
Press button Remote / Local on FDR  then   FDR in Local , press “Run 1”, the motor is running.

Bruno_Hussenet_0-1683289741966.png

 


At your disposal for any further details.
Regards
Bruno

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Jean_Commeignes
Administrator Jean_Commeignes Administrator
Administrator

Posted: ‎2023-04-27 05:51 AM

0 Likes
0
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-27 05:51 AM

Hello TMS, we are looking for the answer...

Best regards

Jean COMMEIGNES
Schneider Electric Community Manager for Power & Building
Reply

Link copied. Please paste this link to share this article on your social media post.

Bruno_Hussenet
Crewman Bruno_Hussenet Crewman
Crewman

Posted: ‎2023-05-05 05:29 AM

1 Like
0
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-05 05:29 AM

Hello TMS,
Sorry for the time taken in responding to your request.
My setup : LTMR08EBD V2.9 + LTMCUF (FDR)
With the following settings in SoMove, Input I6 is wired ON  ,  I can change between L/R with the FDR (LTMCUF).  
Press button Remote / Local on FDR  then   FDR in Local , press “Run 1”, the motor is running.

Bruno_Hussenet_0-1683289741966.png

 


At your disposal for any further details.
Regards
Bruno

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore