Hi,
You could find here a FAQ which explains the steps you need.
From factory setting you need to enter conf menu and set FR1=LCC
Then run and stop buttons on remote terminal will work, but display by default will not show frequency reference. Instead motor speed is displayed.
To change freq setpoint on remote terminal, it is necessary to enter rfr menu and select frh. Then freq reference will remain on HMI. Simultaneously, RFR LED diode on HMI will be lit. If the led diode is not lit, rfr menu is not active (and motor speed is shown on HMI).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-12-03 11:40 PM
Hi,
You could find here a FAQ which explains the steps you need.
From factory setting you need to enter conf menu and set FR1=LCC
Then run and stop buttons on remote terminal will work, but display by default will not show frequency reference. Instead motor speed is displayed.
To change freq setpoint on remote terminal, it is necessary to enter rfr menu and select frh. Then freq reference will remain on HMI. Simultaneously, RFR LED diode on HMI will be lit. If the led diode is not lit, rfr menu is not active (and motor speed is shown on HMI).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.