Posted: 2024-09-18 01:45 AM
If the R1 assignment is set to 'Ready', will the relay R1 energize if inverter is 'Ready'? or de-energize if inverter is 'Ready'? And I searched the manual, it doesn't seem to have a clear statement on the condition for the inverter to be 'Ready', so on and so forth. Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-04 04:28 AM
Dear Temy if you set in ATV71 or ATVProcess R1 or R2 as Ready , relay will swtich from 0->1 only when the drive is in RDY(READY) state , it will be 0 for any other state ( Run, NLP , NST , ACC , DEC ,CLI ,etc) . Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-04 04:28 AM
Dear Temy if you set in ATV71 or ATVProcess R1 or R2 as Ready , relay will swtich from 0->1 only when the drive is in RDY(READY) state , it will be 0 for any other state ( Run, NLP , NST , ACC , DEC ,CLI ,etc) . Thank you