I have an ATV71E5D55N4 vfd drives a service lift with high moment of inertia,
I can not calculate load moment of inertia and gear ratio to calculate exact braking resistor value and power, so what is the recomended braking resistor value for ATV71E5D55N4?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-17 09:32 AM
A rapid and efficient way to determine a braking resistor on Hoisting system is to use the half of motor power on power resistance, it means in you case if you have a 55kW motor, I would suggest a 25 kW resistor will be enough, regarding the ohmic resistor, I advise you to have a look in the documentation where mini value are indicated.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-17 09:32 AM
A rapid and efficient way to determine a braking resistor on Hoisting system is to use the half of motor power on power resistance, it means in you case if you have a 55kW motor, I would suggest a 25 kW resistor will be enough, regarding the ohmic resistor, I advise you to have a look in the documentation where mini value are indicated.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.