We installed ATV610d55n4 Drive.And run upto 1200 hrs.Now we try to run,HMI display getting OFF&ON,while giving run command....why it's happening... ???? and in display not showing any errors,it's show RDY.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-09 08:56 AM
This is minor issue affecting the Whole Drive.
When the FAN was failed,HMI displaying RDY Mode and when we try to give RUN command,VFD display getting OFF and ON.
After removing FAN connection that issue will not repeat,Drive RUN asusual but thermal state will increase.