Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Get support to configure, troubleshoot, update or upgrade your motor management solution built with Altivar variable speed drives and Tesys devices to start, control, protect and monitor Low Voltage and Medium Voltage motors and loads, covering direct start, soft start and variable speed control.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-19 01:11 AM . Last Modified: 2023-06-09 04:21 AM
We installed ATV610d55n4 Drive.And run upto 1200 hrs.Now we try to run,HMI display getting OFF&ON,while giving run command....why it's happening... ???? and in display not showing any errors,it's show RDY.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-09 08:56 AM
This is minor issue affecting the Whole Drive.
When the FAN was failed,HMI displaying RDY Mode and when we try to give RUN command,VFD display getting OFF and ON.
After removing FAN connection that issue will not repeat,Drive RUN asusual but thermal state will increase.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.