ATV6000 with voltage drop 30%
  • Industrial Automation
  • Solutions for Motor Management
  • ATV6000 with voltage drop 30%
BJacqz
Commander BJacqz Commander
49
LeoLazzaro
Lieutenant LeoLazzaro Lieutenant
16
PriscilaCunha22
Lieutenant JG PriscilaCunha22 Lieutenant JG
15
Altivar Process (Medium Voltage)
Back to Solutions for Motor Management
LHNPhuong
LHNPhuong Cadet
Cadet
Posted: ‎2022-04-20 09:54 PM . Last Modified: ‎2023-03-13 06:48 AM
2570
Hi community,
What is the behavior of ATV6000 if supply voltage drop up to -30% ?
In ATV6000 Handbook we know that Drive is de-rated if voltage drop to -25%
However, some competitor provide in their specs that Drive can work with voltage drop -30%
Please advise
  • Design & Build
  • Medium Voltage AC Drives
Daniel_Mougin
Ensign Daniel_Mougin Ensign
Ensign
Posted: ‎2022-04-21 06:10 AM
As the variable speed drives are not designed for a UPS function, they cannot be asked to maintain full load/full speed if the input power in not there or not at the needed level.
However, we have strategies to maintain some level of operation, and most of the competitors (to not say all) go the same way and don't maintain full power at the output.
Firstly, the control is always supplied through an UPS to keep itactive.
Then, for ATV6000, the activation of the "Voltage Dip" function allows to let the motor go freewheeling or slightly regenerating to maintain the energy of the DC bus capacitors to supply the powercells (inverter part) control. This avoids activating the USF fault (undervoltage on DC bus).
The control of the motor can be taken back if the electrical network recovers within a maximum of 30s (settable delay between 0 to 30s).
VSD will then perform a “catch on fly” and re-accelerate the motor to the reference speed according to selected acceleration ramp.
Daniel_Mougin
Ensign