Help
  • Explore Community Expore Community
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Explore Community Explore Community
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • EcoStruxure Asset Advisor
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

What does EwsBindingConfig Timeout Properties represent?

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • What does EwsBindingConfig Timeout Properties represent?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
JeffBowman Schneider Alumni (Retired)
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
mike_meirovitz
Commander mike_meirovitz
21
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SmartConnector Forum
Solved
sesa180961_brid
Lieutenant sesa180961_brid Lieutenant
Lieutenant

Posted: ‎2016-10-11 07:43 AM

0 Likes
8
282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-11 07:43 AM

What does EwsBindingConfig Timeout Properties represent?

I am using the EWS library in my program. I am receiving this error for some of my AS devices when I try to get the EWS Client.

GetEwsClient has an exception for http://xx.xxx.xx.xxx/EcoStruxure/DataExchange. The request channel timed out while waiting for a reply after 00:29:56.9976998. Increase the timeout value passed to the call to Request or increase the SendTimeout value on the Binding. The time allotted to this operation may have been a portion of a longer timeout.. The HTTP request to 'http://xx.xxx.xx.xxx/EcoStruxure/DataExchange' has exceeded the allotted timeout of 00:30:00. The time allotted to this operation may have been a portion of a longer timeout.

I noticed that I can pass my own EwsBindingConfig to this method to overwrite the default timeout. The intellisense only says it takes a double but does not tell if represents seconds or minutes.


Is it timeout seconds or minutes?

Tags (3)
  • Tags:
  • ews
  • ewsbindingconfig
  • timeout
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa180908_brid
Commander sesa180908_brid Commander
Commander

Posted: ‎2016-10-11 07:48 AM

0 Likes
7
256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-11 07:48 AM

Maneesh,

All timeout values are in seconds.

If you use the overloaded constructor for EwsClient which allows you to supply your own binding config I would recommend also using the static EwsClient.DefaultBindingConfig to retrieve the default binding and then update only those properties you need to.




See Answer In Context

Reply
Replies 8
sesa180908_brid
Commander sesa180908_brid Commander
Commander

Posted: ‎2016-10-11 07:48 AM

0 Likes
7
257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-11 07:48 AM

Maneesh,

All timeout values are in seconds.

If you use the overloaded constructor for EwsClient which allows you to supply your own binding config I would recommend also using the static EwsClient.DefaultBindingConfig to retrieve the default binding and then update only those properties you need to.




Reply
JeffBowman
JeffBowman Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2016-10-11 07:53 AM

0 Likes
2
257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-11 07:53 AM

Beyond what Mark has said, it might be worth debugging exactly why you are timing out as well, while changing the default binding config may 'hide' the issue, if SBO is taking over 30 seconds to respond to an EWS request, this is worth noting as it may be a sign of an overloaded system.

Reply
sesa180908_brid
Commander sesa180908_brid Commander
Commander

Posted: ‎2016-10-11 07:59 AM

0 Likes
1
257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-11 07:59 AM

Actually, the default timeout as described above is 30 minutes (not seconds). 

Regardless, Jeff makes a very valid case.  Are you seeing timeouts that are shorter?  If so, then it's not the client that's timing out and changing the value wouldn't matter.

Reply
sesa180908_brid
Commander sesa180908_brid Commander
Commander

Posted: ‎2016-10-11 08:01 AM

0 Likes
0
257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-11 08:01 AM

I'm probably confusing matters.  The timeout property values on the binding is in seconds but the default timeout is actually 1800 (which is 30 minutes worth of timeout).

Reply
sesa180961_brid
Lieutenant sesa180961_brid Lieutenant
Lieutenant

Posted: ‎2016-10-11 08:10 AM

0 Likes
2
257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-11 08:10 AM

Hi Mark,

I could not find the DefaultBindingConfig on the EwsClient.

Could you please share a code snippet?

Reply
sesa180908_brid
Commander sesa180908_brid Commander
Commander

Posted: ‎2016-10-11 08:14 AM

0 Likes
1
257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-11 08:14 AM

What NuGet version are you using?

Reply
sesa180961_brid
Lieutenant sesa180961_brid Lieutenant
Lieutenant

Posted: ‎2016-10-11 08:21 AM

0 Likes
0
257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-11 08:21 AM

I have 1.3.45. I will update to the latest and see if that makes a difference. Thanks!

Reply
sesa180961_brid
Lieutenant sesa180961_brid Lieutenant
Lieutenant

Posted: ‎2016-10-11 08:46 AM

0 Likes
0
257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-11 08:46 AM

That worked. Had to update Ews.Client to the latest (v2.1.83) and here is the code.

          private static EwsBindingConfig _ewsBindingConfig = EwsClient.DefaultBindingConfig;

          // all in seconds

          _ewsBindingConfig.SendTimeout = 60;

            try

            {

                var credentials = new EwsSecurity

                {

                    AuthenticationScheme = AuthenticationSchemes.Digest,

                    Username = username,

                    Password = password

                };

                return new EwsClient(credentials, url, _ewsBindingConfig);

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.