Hi, Webstation 3.2.4 does not show any reading or values on chrome or edge browser, I've cleared my cache and still no input .
Is there any help please
Link copied. Please paste this link to share this article on your social media post.
"MutationEvent is not defined" Javascript errors are displayed after Chromium based browsers (Chrome or Microsoft Edge) are updated to version 127. As referenced in Mutation events will be removed from Chrome | Blog | Chrome for Developers, Google has deprecated these Mutation events and replaced them with a different function.
Hotfixes are available that address the issue or you can apply the temporary mitigations noted below to allow the previous functionality until March 2025.
Google Chrome browser:
MS Edge browser:
Link copied. Please paste this link to share this article on your social media post.
"MutationEvent is not defined" Javascript errors are displayed after Chromium based browsers (Chrome or Microsoft Edge) are updated to version 127. As referenced in Mutation events will be removed from Chrome | Blog | Chrome for Developers, Google has deprecated these Mutation events and replaced them with a different function.
Hotfixes are available that address the issue or you can apply the temporary mitigations noted below to allow the previous functionality until March 2025.
Google Chrome browser:
MS Edge browser: