Hello to all,
in an installation site the admin has been locked out. Is there a time limit for this lock out? Can we restore this password?
Thank you in advance
Sotiris
Link copied. Please paste this link to share this article on your social media post.
Hi Sotiris,
As far as I know, the default lockout time is only 5 minutes.
If you have to wait over 5 minutes. And it seems like it won't unlock. You can do the following:

Regards,
-Jeff
Link copied. Please paste this link to share this article on your social media post.
Hi Sotiris,
As far as I know, the default lockout time is only 5 minutes.
If you have to wait over 5 minutes. And it seems like it won't unlock. You can do the following:

Regards,
-Jeff
Link copied. Please paste this link to share this article on your social media post.
Hello Jeff,
thank you for the answer, indeed after 5 minutes it was unlocked.
Best regards
Sotiris