SmartConnector use problem!?

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • SmartConnector use problem!?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
View All

Recommended Forums

  • Intelligent Devices Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SmartConnector Forum
Start a Topic
Solved
TomeLu
Commander | EcoXpert Master TomeLu Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2021-11-07 11:48 PM

0 Likes
6
1941
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-11-07 11:48 PM

SmartConnector use problem!?

I use SmartConnector for the first time
I currently want to try the SmartConnector function
Just got a new account and installed the software
Download the certification on the SmartConnector webpage
Upload to local computer
Always say that my approval has expired! ?
I want to ask what is the reason?

未命名.jpg

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TomeLu
Commander | EcoXpert Master TomeLu Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2021-11-09 06:12 PM

0 Likes
1
1910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-11-09 06:12 PM

Hi , @ardak 

 

Thank you for your help
I try to reinstall the SmartConnect program
At present, the certification has been uploaded successfully, and other functions can be operated
If you still have any questions after trying, I will ask again
thanks

 

未命名.jpg

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 6
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-11-08 12:48 AM

1 Like
5
1937
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-11-08 12:48 AM

Hi,

 

----> Download the certification on the SmartConnector webpage

 

Please elaborate on the steps taken during this step, this is probably where the issue lies.

 

BR

Armend

Tags (1)
  • Tags:
  • english
Reply
TomeLu
Commander | EcoXpert Master TomeLu Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2021-11-08 05:11 PM

0 Likes
4
1934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-11-08 05:11 PM

Hi @ardak  

 

I use Runtime 2.4 (Developer) as a demonstration, here are my steps
1. Log in to the local Smart Connecrtor
2. Copy "Machine Fingerprint"
3. Log in to the SmartConnector server
4. Click Runtime 2.4 (Developer)
5. Paste "machine fingerprint"
6. Successfully downloaded Smart Connector 2.4 Core (Developer).lic
7. Upload to the local Smart Connector
8. Show that my certificate has expired

Is there a problem with my steps?
thanks for your help

Tags (1)
  • Tags:
  • english
Reply
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-11-08 10:19 PM

1 Like
3
1927
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-11-08 10:19 PM

Ok!

 

Could you please go to the portal -> setup -> service settings and set the logging level to trace, try to upload the license again and attach the logs?

 

They are located in %programdata%\Smartconnector\Logs

 

BR

Armend

Tags (1)
  • Tags:
  • english
Reply
TomeLu
Commander | EcoXpert Master TomeLu Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2021-11-09 01:29 AM

0 Likes
0
1923
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-11-09 01:29 AM

Hi @ardak 

I followed the method you said
SmartConnector has been set up
Also successfully found the Logs record
The following is the recorded content

------------------------------------------------------------------------------------------------------------------------------------------------------------------------------

2021-11-09 17:22:31.2881,Error,Service,<no principal>,Padding is invalid and cannot be removed.
at System.Security.Cryptography.RijndaelManagedTransform.DecryptData(Byte[] inputBuffer, Int32 inputOffset, Int32 inputCount, Byte[]& outputBuffer, Int32 outputOffset, PaddingMode paddingMode, Boolean fLast)
at System.Security.Cryptography.RijndaelManagedTransform.TransformFinalBlock(Byte[] inputBuffer, Int32 inputOffset, Int32 inputCount)
at SxL.Common.Crypto.Decrypt(String value, String keyValue, String initializationVector)
at Mongoose.Common.Data.ExtensionMethods.Decrypt(IEncryptable encryptable, String encryptionKey)
at Mongoose.Service.Data.MongooseDbContext.OnObjectMaterialized(Object sender, ObjectMaterializedEventArgs e)
at System.Data.Entity.Core.Objects.ObjectContext.OnObjectMaterialized(Object entity)
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper.RaiseMaterializedEvents()
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper`1.StopMaterializingElement()
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper`1.SimpleEnumerator.MoveNext()
at System.Linq.Enumerable.FirstOrDefault[TSource](IEnumerable`1 source)
at Mongoose.Service.Licensing.AntiRollbackDateTime.get_UtcNow()
,["Current WindowsIdentity is NT AUTHORITY\\SYSTEM"],
2021-11-09 17:22:31.2881,Trace,Service,<no principal>,Validating framework license,
2021-11-09 17:22:36.3064,Error,Service,<no principal>,Padding is invalid and cannot be removed.
at System.Security.Cryptography.RijndaelManagedTransform.DecryptData(Byte[] inputBuffer, Int32 inputOffset, Int32 inputCount, Byte[]& outputBuffer, Int32 outputOffset, PaddingMode paddingMode, Boolean fLast)
at System.Security.Cryptography.RijndaelManagedTransform.TransformFinalBlock(Byte[] inputBuffer, Int32 inputOffset, Int32 inputCount)
at SxL.Common.Crypto.Decrypt(String value, String keyValue, String initializationVector)
at Mongoose.Common.Data.ExtensionMethods.Decrypt(IEncryptable encryptable, String encryptionKey)
at Mongoose.Service.Data.MongooseDbContext.OnObjectMaterialized(Object sender, ObjectMaterializedEventArgs e)
at System.Data.Entity.Core.Objects.ObjectContext.OnObjectMaterialized(Object entity)
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper.RaiseMaterializedEvents()
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper`1.StopMaterializingElement()
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper`1.SimpleEnumerator.MoveNext()
at System.Linq.Enumerable.FirstOrDefault[TSource](IEnumerable`1 source)
at Mongoose.Service.Licensing.AntiRollbackDateTime.get_UtcNow()
,["Current WindowsIdentity is NT AUTHORITY\\SYSTEM"],
2021-11-09 17:22:36.3064,Trace,Service,<no principal>,Validating framework license,
2021-11-09 17:22:41.3347,Error,Service,<no principal>,Padding is invalid and cannot be removed.
at System.Security.Cryptography.RijndaelManagedTransform.DecryptData(Byte[] inputBuffer, Int32 inputOffset, Int32 inputCount, Byte[]& outputBuffer, Int32 outputOffset, PaddingMode paddingMode, Boolean fLast)
at System.Security.Cryptography.RijndaelManagedTransform.TransformFinalBlock(Byte[] inputBuffer, Int32 inputOffset, Int32 inputCount)
at SxL.Common.Crypto.Decrypt(String value, String keyValue, String initializationVector)
at Mongoose.Common.Data.ExtensionMethods.Decrypt(IEncryptable encryptable, String encryptionKey)
at Mongoose.Service.Data.MongooseDbContext.OnObjectMaterialized(Object sender, ObjectMaterializedEventArgs e)
at System.Data.Entity.Core.Objects.ObjectContext.OnObjectMaterialized(Object entity)
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper.RaiseMaterializedEvents()
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper`1.StopMaterializingElement()
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper`1.SimpleEnumerator.MoveNext()
at System.Linq.Enumerable.FirstOrDefault[TSource](IEnumerable`1 source)
at Mongoose.Service.Licensing.AntiRollbackDateTime.get_UtcNow()
,["Current WindowsIdentity is NT AUTHORITY\\SYSTEM"],
2021-11-09 17:22:41.3347,Trace,Service,<no principal>,Validating framework license,
2021-11-09 17:22:46.3610,Error,Service,<no principal>,Padding is invalid and cannot be removed.
at System.Security.Cryptography.RijndaelManagedTransform.DecryptData(Byte[] inputBuffer, Int32 inputOffset, Int32 inputCount, Byte[]& outputBuffer, Int32 outputOffset, PaddingMode paddingMode, Boolean fLast)
at System.Security.Cryptography.RijndaelManagedTransform.TransformFinalBlock(Byte[] inputBuffer, Int32 inputOffset, Int32 inputCount)
at SxL.Common.Crypto.Decrypt(String value, String keyValue, String initializationVector)
at Mongoose.Common.Data.ExtensionMethods.Decrypt(IEncryptable encryptable, String encryptionKey)
at Mongoose.Service.Data.MongooseDbContext.OnObjectMaterialized(Object sender, ObjectMaterializedEventArgs e)
at System.Data.Entity.Core.Objects.ObjectContext.OnObjectMaterialized(Object entity)
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper.RaiseMaterializedEvents()
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper`1.StopMaterializingElement()
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper`1.SimpleEnumerator.MoveNext()
at System.Linq.Enumerable.FirstOrDefault[TSource](IEnumerable`1 source)
at Mongoose.Service.Licensing.AntiRollbackDateTime.get_UtcNow()
,["Current WindowsIdentity is NT AUTHORITY\\SYSTEM"],
2021-11-09 17:22:46.3610,Trace,Service,<no principal>,Validating framework license,
2021-11-09 17:22:51.3812,Error,Service,<no principal>,Padding is invalid and cannot be removed.
at System.Security.Cryptography.RijndaelManagedTransform.DecryptData(Byte[] inputBuffer, Int32 inputOffset, Int32 inputCount, Byte[]& outputBuffer, Int32 outputOffset, PaddingMode paddingMode, Boolean fLast)
at System.Security.Cryptography.RijndaelManagedTransform.TransformFinalBlock(Byte[] inputBuffer, Int32 inputOffset, Int32 inputCount)
at SxL.Common.Crypto.Decrypt(String value, String keyValue, String initializationVector)
at Mongoose.Common.Data.ExtensionMethods.Decrypt(IEncryptable encryptable, String encryptionKey)
at Mongoose.Service.Data.MongooseDbContext.OnObjectMaterialized(Object sender, ObjectMaterializedEventArgs e)
at System.Data.Entity.Core.Objects.ObjectContext.OnObjectMaterialized(Object entity)
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper.RaiseMaterializedEvents()
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper`1.StopMaterializingElement()
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper`1.SimpleEnumerator.MoveNext()
at System.Linq.Enumerable.FirstOrDefault[TSource](IEnumerable`1 source)
at Mongoose.Service.Licensing.AntiRollbackDateTime.get_UtcNow()
,["Current WindowsIdentity is NT AUTHORITY\\SYSTEM"],
2021-11-09 17:22:51.3812,Trace,Service,<no principal>,Validating framework license,
2021-11-09 17:22:54.5054,Error,Service,admin,Padding is invalid and cannot be removed.
at System.Security.Cryptography.RijndaelManagedTransform.DecryptData(Byte[] inputBuffer, Int32 inputOffset, Int32 inputCount, Byte[]& outputBuffer, Int32 outputOffset, PaddingMode paddingMode, Boolean fLast)
at System.Security.Cryptography.RijndaelManagedTransform.TransformFinalBlock(Byte[] inputBuffer, Int32 inputOffset, Int32 inputCount)
at SxL.Common.Crypto.Decrypt(String value, String keyValue, String initializationVector)
at Mongoose.Common.Data.ExtensionMethods.Decrypt(IEncryptable encryptable, String encryptionKey)
at Mongoose.Service.Data.MongooseDbContext.OnObjectMaterialized(Object sender, ObjectMaterializedEventArgs e)
at System.Data.Entity.Core.Objects.ObjectContext.OnObjectMaterialized(Object entity)
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper.RaiseMaterializedEvents()
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper`1.StopMaterializingElement()
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper`1.SimpleEnumerator.MoveNext()
at System.Linq.Enumerable.FirstOrDefault[TSource](IEnumerable`1 source)
at Mongoose.Service.Licensing.AntiRollbackDateTime.get_UtcNow()
,["Current WindowsIdentity is NT AUTHORITY\\SYSTEM"],
2021-11-09 17:22:54.6094,Error,Service,admin,Padding is invalid and cannot be removed.
at System.Security.Cryptography.RijndaelManagedTransform.DecryptData(Byte[] inputBuffer, Int32 inputOffset, Int32 inputCount, Byte[]& outputBuffer, Int32 outputOffset, PaddingMode paddingMode, Boolean fLast)
at System.Security.Cryptography.RijndaelManagedTransform.TransformFinalBlock(Byte[] inputBuffer, Int32 inputOffset, Int32 inputCount)
at SxL.Common.Crypto.Decrypt(String value, String keyValue, String initializationVector)
at Mongoose.Common.Data.ExtensionMethods.Decrypt(IEncryptable encryptable, String encryptionKey)
at Mongoose.Service.Data.MongooseDbContext.OnObjectMaterialized(Object sender, ObjectMaterializedEventArgs e)
at System.Data.Entity.Core.Objects.ObjectContext.OnObjectMaterialized(Object entity)
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper.RaiseMaterializedEvents()
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper`1.StopMaterializingElement()
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper`1.SimpleEnumerator.MoveNext()
at System.Linq.Enumerable.FirstOrDefault[TSource](IEnumerable`1 source)
at Mongoose.Service.Licensing.AntiRollbackDateTime.get_UtcNow()
,["Current WindowsIdentity is NT AUTHORITY\\SYSTEM"],
2021-11-09 17:22:54.6094,Debug,Utility,admin,MayNotContinue : Your license has expired. Please contact your distributor/vendor to renew the license.,
2021-11-09 17:22:56.4015,Error,Service,<no principal>,Padding is invalid and cannot be removed.
at System.Security.Cryptography.RijndaelManagedTransform.DecryptData(Byte[] inputBuffer, Int32 inputOffset, Int32 inputCount, Byte[]& outputBuffer, Int32 outputOffset, PaddingMode paddingMode, Boolean fLast)
at System.Security.Cryptography.RijndaelManagedTransform.TransformFinalBlock(Byte[] inputBuffer, Int32 inputOffset, Int32 inputCount)
at SxL.Common.Crypto.Decrypt(String value, String keyValue, String initializationVector)
at Mongoose.Common.Data.ExtensionMethods.Decrypt(IEncryptable encryptable, String encryptionKey)
at Mongoose.Service.Data.MongooseDbContext.OnObjectMaterialized(Object sender, ObjectMaterializedEventArgs e)
at System.Data.Entity.Core.Objects.ObjectContext.OnObjectMaterialized(Object entity)
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper.RaiseMaterializedEvents()
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper`1.StopMaterializingElement()
at System.Data.Entity.Core.Common.Internal.Materialization.Shaper`1.SimpleEnumerator.MoveNext()
at System.Linq.Enumerable.FirstOrDefault[TSource](IEnumerable`1 source)
at Mongoose.Service.Licensing.AntiRollbackDateTime.get_UtcNow()
,["Current WindowsIdentity is NT AUTHORITY\\SYSTEM"],
2021-11-09 17:22:56.4015,Trace,Service,<no principal>,Validating framework license,未命名.jpg

Tags (1)
  • Tags:
  • english
Reply
TomeLu
Commander | EcoXpert Master TomeLu Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2021-11-09 06:12 PM

0 Likes
1
1911
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-11-09 06:12 PM

Hi , @ardak 

 

Thank you for your help
I try to reinstall the SmartConnect program
At present, the certification has been uploaded successfully, and other functions can be operated
If you still have any questions after trying, I will ask again
thanks

 

未命名.jpg

Tags (1)
  • Tags:
  • english
Reply
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-11-09 09:21 PM

1 Like
0
1908
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-11-09 09:21 PM

I'm glad you could make it work!

 

BR

Armend

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore