SmartConnector extension working with Enterprise central

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • SmartConnector extension working with Enterprise central
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
ardak
ardak Schneider Alumni (Retired)
34
sesa180908_brid
Commander sesa180908_brid Commander
34
mike_meirovitz
Commander mike_meirovitz
21
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to SmartConnector Forum
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2021-10-31 02:07 AM

0 Likes
1
374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-10-31 02:07 AM

SmartConnector extension working with Enterprise central

Hi,

 

I am trying to set our SmartConnector extension to work with the Enterprise Central.

 

When the EWS address is "http://localhost:82/EcoStruxure/DataExchange" (the Enterprise Server), the processor works fine.

When the EWS address is "http://localhost:81/EcoStruxure/DataExchange" (the Enterprise Central), the processor fails. See the errors below from the SmartConnector log file.

 

2021-10-31 11:02:26.0170,Error,EwsConsume,<no principal>,The HTTP request is unauthorized with client authentication scheme 'Digest'. The authentication header received from the server was 'Digest realm="ews@SxWBM",qop="auth",algorithm="SHA-256",nonce="9C82FAD03DBB711B69CFD6078AA47D48E950EE1FBCFB37D83952BF87660AF24C79493CE5714D549DB869CAF1",opaque="C3F3E3"'.
The remote server returned an error: (401) Unauthorized.

 

2021-10-31 11:02:26.0170,Error,Processor,<no principal>,EBO Alarm Item Discovery Processor,System.ServiceModel.Security.MessageSecurityException: The HTTP request is unauthorized with client authentication scheme 'Digest'. The authentication header received from the server was 'Digest realm="ews@SxWBM",qop="auth",algorithm="SHA-256",nonce="9C82FAD03DBB711B69CFD6078AA47D48E950EE1FBCFB37D83952BF87660AF24C79493CE5714D549DB869CAF1",opaque="C3F3E3"'. ---> System.Net.WebException: The remote server returned an error: (401) Unauthorized.
at System.Net.HttpWebRequest.GetResponse()
at System.ServiceModel.Channels.HttpChannelFactory`1.HttpRequestChannel.HttpChannelRequest.WaitForReply(TimeSpan timeout)

 

Any idea what is causing the error?

 

Thanks,

 

Michael

 

 

 

 

 

Attachments
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-11-02 02:08 AM

0 Likes
0
369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-11-02 02:08 AM

Hi,

 

Check that your password is correct on the EC.

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.