SmartConnector Weather Service - step-by-step guide

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • SmartConnector Weather Service - step-by-step guide
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
View All

Recommended Forums

  • Intelligent Devices Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SmartConnector Forum
Start a Topic
Solved
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2019-11-30 09:58 PM

0 Likes
8
3613
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-30 09:58 PM

SmartConnector Weather Service - step-by-step guide

Hi,

I am looking for a step-by-step guide that explains how to define the EWS server in the EBO. I am using EBO 3.0.

To be more specific, what should be the values of the following fields?

EWS Server.png

 

Thank you.

Mike

Tags (1)
  • Tags:
  • EWS Weather Extension
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2020-02-07 02:02 AM

1 Like
0
3538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-07 02:02 AM

Hi @mike_meirovitz,

 

@Anonymous user helped you to solve your problem. Please click on “Accept as Solution” so other members can find the same solution through the search bar.

 

Thank you!

See Answer In Context

Reply
Replies 8
Anonymous user
Not applicable

Posted: ‎2019-12-02 06:45 AM

0 Likes
5
3607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-02 06:45 AM

There is currently no guide (that I know of) that goes over defining the server in EBO; however, it is a quick process.

The address for your EWS server should look something like http://localhost:PORT#/EcoStruxure/DataExchange, or something similar, depends how it was configured in the Processor Configuration.

 

With that in mind, here is what the fields should have:

1. EWS Server: localhost

2. Protocol: HTTP, EWS Communication Port: PORT#

3. EWS Path: EcoStruxure/DataExchange

4. The username and password are whatever was defined for the username and password for the EWS server (this was specified in the configuration of the Setup Processor).

Tags (1)
  • Tags:
  • server
Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2019-12-02 08:48 AM

0 Likes
4
3603
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-02 08:48 AM

Hi Nick,

 

Thank you for your answer. I have followed your steps. When I browse the tree in the EBO, and reach System > Hardware > EcoStruxure Web Services > EcoStruxure Web Service_Weather, I get an error. See below. Any idea what is wrong?

 

Thank you!

Mike

 

Capture.JPG

Reply
Anonymous user
Not applicable

Posted: ‎2019-12-02 10:21 AM

0 Likes
3
3600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-02 10:21 AM

Check the EWS server on the Smart Connector web portal to see if it is running. Assuming you typed in the correct details for the interface, the problem lies with the server having not started.

Go to the server under the EWS Server tab and hit the play icon (although, it should have started upon creation). If it is running, that icon will turn into a square "Stop" icon.

If it does not play, consult the logs under C:\Program Data\SmartConnector\Logs (enable "View hidden items" in Windows Explorer to find the Program Data folder).

Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2019-12-03 09:38 PM

0 Likes
2
3597
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-03 09:38 PM

Hi Nick,

 

The EWS is running. See below.

Capture.JPG

 

See the relevant part of the SmartConnector log file:

2019-12-04 06:52:05.1146,Debug,Service,<no principal>,MayNotContinue : The license you are attempting to use was not created for this machine.,
2019-12-04 06:52:05.2551,Info,WorkerThread,<no principal>,Weather Update Processor,Started,
2019-12-04 06:52:05.2864,Debug,WorkerThread,<no principal>,Weather Update Processor,InstantiateProcessor,ET=31 mSec,
2019-12-04 06:52:05.3645,Debug,WorkerThread,<no principal>,Weather Update Processor,Execute (start),2019-12-04T04:52:05,
2019-12-04 06:52:05.3645,Debug,Processor,<no principal>,Processor Weather Update Processor Execute started,
2019-12-04 06:52:05.5208,Error,Processor,<no principal>,The supplied value is not consistent with the ValueItem's Type property.
at Mongoose.Ews.Server.Data.EwsServerDataAdapter.ModifyValueItemValue(EwsValueItem toModify, Nullable`1 newValue, Nullable`1 newState)
at SmartConnector.WeatherExtension.UpdateProcessor.DoUpdateCurrentConditions(Int64 cityId)
at SmartConnector.WeatherExtension.UpdateProcessor.DoUpdates(Int64 cityId)
at CallSite.Target(Closure , CallSite , UpdateProcessor , Object )
at SmartConnector.WeatherExtension.UpdateProcessor.Execute_Subclass()
at Mongoose.Process.Processor.Execute(CancellationToken token, ProcessorExecutionMode mode)
,["Weather Update Processor"],
2019-12-04 06:52:05.5208,Debug,Processor,<no principal>,Processor Weather Update Processor Execute completed,

 

I see 2 problems:

1. license issue. My SmartConnector license seems to be valid...

2. Error,Processor,<no principal>,The supplied value is not consistent with the ValueItem's Type property. Do you understand what is wrong?

 

Thanks!

Mike

 

 

Reply
Anonymous user
Not applicable

Posted: ‎2019-12-04 07:00 AM . Last Modified: ‎2019-12-04 07:05 AM

0 Likes
1
3592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-04 07:00 AM

Interesting. I have only seen this issue as a result of incorrect configuration or a stopped server. Are you following the training and going through the steps to make and deploy the processor yourself?

Unfortunately, the log excerpt you showed me doesn't help; it shows issues with the Update Processor, not the EWS Server. What you would want to do now is turn on EWS Consume Logging. To do this, in the Smart Connector Web portal, go to Setup -> Logging Filters. Also, set logging level to Trace (Setup -> Service Settings).

 

As for the errors you are seeing in the log:

1. I have not had this error before. My assumption is that you created the license incorrectly on SmartConnectorServer.com, or are using a license that someone else made for themselves. If you are indeed following the training, go through the licensing section step-by-step.

2. The update processor is trying to update Int64 CityId with a value that is not of type Int64, this indicates a programming error in the Update Processor.

Reply
mike_meirovitz
Commander mike_meirovitz
Commander

Posted: ‎2019-12-04 09:06 AM

0 Likes
0
3586
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-04 09:06 AM

Hi Nick,

 

Thank you for your answer. Logging Level is already set to Trace. Ews Consume is already set to True.

 

We will check the Update Processor for the CityId variable.

 

Thank you!

 

Mike

Reply
Anonymous user
Not applicable

Posted: ‎2020-02-07 02:02 AM

1 Like
0
3539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-07 02:02 AM

Hi @mike_meirovitz,

 

@Anonymous user helped you to solve your problem. Please click on “Accept as Solution” so other members can find the same solution through the search bar.

 

Thank you!

Reply
Christopherrrr
Crewman Christopherrrr
Crewman

Posted: ‎2024-11-18 02:06 AM

0 Likes
0
1796
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-18 02:06 AM

Where can i find the license to use with my OpenWeather processor that i have installed

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore