Smart Connector: https end point using https data source with self signed certificate

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • Smart Connector: https end point using https data source with self signed certificate
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
View All

Recommended Forums

  • Intelligent Devices Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SmartConnector Forum
Start a Topic
Solved
ChrisLaurentius
ChrisLaurentius Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2018-06-11 08:17 PM

0 Likes
2
1482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-06-11 08:17 PM

Smart Connector: https end point using https data source with self signed certificate

Hi,

Continuation of:

Smart Connector: http end point using https data source with self signed certificate

Just in case customer requires Smart Connector's end point to be in https as well.

I've got the following message when binding the ssl certificate using netsh:

Following Smart Connector installation guide on Configuring HTTPS on SmartConnector Endpoints (page 87/88)

Tried the ID stated in Adam Summers​ post as well: EWS RESTful EWS Gateway binding with HTTPS

Setup:

Smart Connector version SmartConnector-2.3.117 with ISC.CustomSoapRestProvider.dll

Data source: DCE 750 on https only using self signed certificate.

Steps:

1.Downloaded DCE's self signed certificate from browser

2.Skipped the steps on Bundle the received certificate with the private key; this is a self signed certificate

     If this step is needed, how do I get the private key, CSR of self signed certificate from say SBO, PME & DCE?

3.Added DCE.cer to both Local Computer's Personal Certificate

4. Defined https end point in smart connector

5. Ran netsh againts DCE self signed certificate's thumbprint, using both appid 596e502c-7957-4a02-8167-716d19ced67f (per manual), and the one service GUID suggested on the Adam's thread: 0268946a-3985-46f9-a9c2-cd4016ac6ddb. Both showed the same SSL certificate add failed.

Tags (4)
  • Tags:
  • dce
  • ews
  • https
  • smartconnector
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa178151_brid
Crewman sesa178151_brid Crewman
Crewman

Posted: ‎2018-06-13 09:31 AM

1 Like
1
1443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-06-13 09:31 AM

I haven't used this particular extension, but if you want SC to serve https, then you'll need to create a dedicated cert for the server on which SC is running. You can't take the DCE cert or any other cert from another server and install it on the SC server to serve. At a minimum, the server name won't match (unless SC and DCE are on the same server).

As Adam explained, you would install the DCE/SBO/PME cert on the SC server when the cert is self-signed, but this is for SC as a client, not a server. This is only b/c it's self-signed and SC won't trust the cert unless it's in the local store.

Separately, you'll need to generate a cert (presumably self-signed) for the SC server and install that in the cert store per the SC instructions. When generating that cert, you'll also need to provide a private key. So, you'll know what value that is.

Hope this helps.

Brett

See Answer In Context

Reply
Replies 2
sesa178151_brid
Crewman sesa178151_brid Crewman
Crewman

Posted: ‎2018-06-13 09:31 AM

1 Like
1
1444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-06-13 09:31 AM

I haven't used this particular extension, but if you want SC to serve https, then you'll need to create a dedicated cert for the server on which SC is running. You can't take the DCE cert or any other cert from another server and install it on the SC server to serve. At a minimum, the server name won't match (unless SC and DCE are on the same server).

As Adam explained, you would install the DCE/SBO/PME cert on the SC server when the cert is self-signed, but this is for SC as a client, not a server. This is only b/c it's self-signed and SC won't trust the cert unless it's in the local store.

Separately, you'll need to generate a cert (presumably self-signed) for the SC server and install that in the cert store per the SC instructions. When generating that cert, you'll also need to provide a private key. So, you'll know what value that is.

Hope this helps.

Brett

Reply
ChrisLaurentius
ChrisLaurentius Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2018-06-17 10:30 PM

0 Likes
0
1443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-06-17 10:30 PM

Thanks Brett,

Will try generating self signed certificate for the SC server itself.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore