@mustafakamalm07 I have attached the latest version of the application note for Avigilon which we can integrate using Security Expert software. I have checked in Security Expert and I can not see a way of linking a camera alarm to an output as you would require this so that the points could be exposed via EWS. The camera alarms are used in Security Expert to trigger an event. The SmartConnector which is mentioned above is for linking Security Expert with EBO and is available on the Exchange market place.
https://shop.exchange.se.com/en-US/apps/73802/ecostruxure-security-expert-smartconnector
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Mustafa,
It all depends on what you want to do. I am not familiar with Avigilon, but based on your images you would need to create a Smartconnector extension that uses their API in the way you need. Realistically this requires prior software development experience.
Someone might have already created a solution you could create, but I am not aware of one. Someone else might have more information here.
BR
Armend
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi adrak,
Thanks for your response and details.
We want to know the status and alarms of cameras to monitor as available in the API.
if there are some guidelines in sbo how to connect the api ?
regards,
Mustafa
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Mustafa,
From what I can see, there is no easy way to do this with only SBO/EBO.
As mentioned before, you would need to use Smartconnector and a custom extension to act as a middle man between the systems. You could do this by getting the values/alarms you need in your extension and exposing them in a Smartconnector EWS server and connect to that EWS server with the SBO/EBO EWS client.
This is not trivial work(as in if there is no ready-made extension available it would need to be developed) and would need to be done by a software developer, either within Schneider or external.
BR
Armend
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
What could be a solution is to use EcoStruxure Security Expert, there is a Avigilon module available for this, and via the existing SmartConnector for Security Expert we might be able to integrate what you need, however i'm not fully know with any limitations but @AdamWright should know this. Adam do you see limitations on receiving status and alarms of cameras through the Avigilon module in Security Expert and publish it to EBO via the Security Expert SmartConnector?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Thank you @Erwin-vd-Zwart and @ardak for your response.
@AdamWright Please can you share the limitations and the smart connector?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
@mustafakamalm07 I have attached the latest version of the application note for Avigilon which we can integrate using Security Expert software. I have checked in Security Expert and I can not see a way of linking a camera alarm to an output as you would require this so that the points could be exposed via EWS. The camera alarms are used in Security Expert to trigger an event. The SmartConnector which is mentioned above is for linking Security Expert with EBO and is available on the Exchange market place.
https://shop.exchange.se.com/en-US/apps/73802/ecostruxure-security-expert-smartconnector