I can't login in the localhost:8082
Hi, i don't know why i can't login in Smartconnector localhost with my user, when i try to login there is a message it say "The user name or password were incorrect" but i didn't change anything, actually i logged yesterday with no problems.
Link copied. Please paste this link to share this article on your social media post.
2024-11-2710:08 AM
Hi Roberto, in the past this is what has worked for me:
You will need to have access to SQL Management Studio application to connect to the SQL instance where the SmartConnector server is, you have two databases in your configuration - a service database (SmartConnector.Service) and a user database (SmartConnector.User) - then take the following steps.
- Stop the Smart Connector Service
- Delete the user database (SmartConnector.User)
- Start the Smart Connector service
This will reset the password back to the default password.