Hello!
We are looking for a method (or technique) to trigger an EBO alarm when an extension's Update Processor is not running.
Thanks!
Ellis
Link copied. Please paste this link to share this article on your social media post.
Hi,
I have not tried to do so myself, but given that you have an Smartconnector EWS server exposed and your updateprocessor runs on a schedule, you could expose a "LastUpdated" value that gets updated by the UpdateProcessor, and then have a EBO Script program that parses the DateTime and triggers an alarm if a time threshold between updates is passed?
BR
Armend