Historical data difference between sql database and SBO

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • Historical data difference between sql database and SBO
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
ardak
ardak Schneider Alumni (Retired)
34
sesa180908_brid
Commander sesa180908_brid Commander
34
mike_meirovitz
Commander mike_meirovitz
21
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SmartConnector Forum
Solved
sesa379286_brid
Ensign sesa379286_brid Ensign
Ensign

Posted: ‎2019-04-15 03:32 AM . Last Modified: ‎2019-04-15 03:33 AM

0 Likes
3
994
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-15 03:32 AM

Historical data difference between sql database and SBO

Hello to group,

 

using the libraries of SmartConnector we are saving manually historical data for a specific processor. Analyzing the SQL database I can see that the data are saved correctly. However, when the historical data are loaded in EBO I can see a difference of 2 hours (the data in SBO arrive 2 hours later, with a timestamp different of 2 hour).

 

A first estimation is the change between UTC and CEST which is 2 hours. Do you have an indication on how to solve this matter?

 

I attach an example of how the data are saved in the database.

 

SmartConnector Version 2.3.118

SBO version 1.9.3.24

 

Thank you in advance

 

Sotirios

Attachments
Tags (2)
  • Tags:
  • HistoryRecords
  • smartconnector
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2019-04-15 05:19 AM

0 Likes
2
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-15 05:19 AM

Hi Sotirios,

 

You are correct, both EWS and EBO use UTC behind the scenes for time stamp transfer. 

 

Are you saving your manual timestamps with UTC or CEST?

 

If you are saving your timestamps in CEST, you will need to convert it to UTC before saving it in the Smart Connector database.

 

Also, EBO will display all times converted from UTC for the timezone of the WorkStation that has logged into it. 

 

Best Regards,

 

-Jeff

See Answer In Context

Reply
Replies 3
JeffBowman
Sisko JeffBowman Sisko
Sisko

Posted: ‎2019-04-15 05:19 AM

0 Likes
2
987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-15 05:19 AM

Hi Sotirios,

 

You are correct, both EWS and EBO use UTC behind the scenes for time stamp transfer. 

 

Are you saving your manual timestamps with UTC or CEST?

 

If you are saving your timestamps in CEST, you will need to convert it to UTC before saving it in the Smart Connector database.

 

Also, EBO will display all times converted from UTC for the timezone of the WorkStation that has logged into it. 

 

Best Regards,

 

-Jeff

Reply
sesa379286_brid
Ensign sesa379286_brid Ensign
Ensign

Posted: ‎2019-04-15 11:25 PM

0 Likes
0
981
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-15 11:25 PM

Hello Jeff, 

 

thank you for the immediate feedback. I will try it this days updating our source code and I will let you know as soon as I have a positive result. 

 

Best regards

 

Sotiris

Reply
sesa379286_brid
Ensign sesa379286_brid Ensign
Ensign

Posted: ‎2019-04-28 01:03 AM

0 Likes
0
971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-04-28 01:03 AM

Hello Jeff,

 

I have tested the change of timestamp from local (CEST in my case) to UTC and I can see the data correctly arriving on my workstation/ webstation. 

 

I will consider this to update my source codes to adjust for historical data and real-time timestamp variables from the SmartConnector database.

 

Thank you for the help

 

Best regards

 

Sotiris

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of