We are using EBO 3.1 and smart connectors 2.4
We try to extract data from EBO using EWS
In smart connector We have used value id to extract value from EBO, we can read the values in smart connector
But while polling it takes single value polling, so it takes long time to poll all values
So, we need to use container id to extract values in Smart connector
Please advise as the procedure extract the values in smart connector from EBO using container id
Or suggest as the possible ways for group polling
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Have you tried:
GET/Containers/{id}/Children?type=value
Steve
Link copied. Please paste this link to share this article on your social media post.
Hi Sir,
Thank You
We will try this and update the status