Getting started with SmartConnector / mongoose.processor (403 forbidden error)

SmartConnector Forum

Schneider Electric support forum about SmartConnector applications for integration of other building management systems (BMS) into EcoStruxure Building Operation.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • SmartConnector
  • SmartConnector Forum
  • Getting started with SmartConnector / mongoose.processor (403 forbidden error)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
JeffBowman
Sisko JeffBowman Sisko
164
sesa180908_brid
Commander sesa180908_brid Commander
34
ardak
ardak Schneider Alumni (Retired)
34
View All

Recommended Forums

  • Intelligent Devices Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to SmartConnector Forum
Start a Topic
Solved
David_Glasgow
Ensign David_Glasgow Ensign
Ensign

Posted: ‎2022-06-22 12:39 PM

0 Likes
5
3096
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-22 12:39 PM

Getting started with SmartConnector / mongoose.processor (403 forbidden error)

Hello community,

I am a newbie to SmartConnector and have started the training sessions.

I am currently on 

  • Smart Connector Setup Processor Configuration: Chapter 4

 

When I attempt to add a reference to mongoose.processor, using the nuget pacakage manager in visual studio.  It is showing a 403 error (forbidden error).

Is there something I need to configure for proxy settings ???

 

NOTE - I have removed my API key from the URL below.

 

[SmartConnector] The V2 feed at 'https://www.myget.org/F/mongoose/auth/MyGETAPIKey/api/v2/Search()?$filter=IsLatestVersion&searchTerm='mongoose.processor'&targetFramework='uap10.0.17763'&includePrerelease=false&$skip=0&$top=26&semVerLevel=2.0.0' returned an unexpected status code '403 Forbidden'.

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
David_Glasgow
Ensign David_Glasgow Ensign
Ensign

Posted: ‎2022-06-23 10:45 AM

0 Likes
1
3031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-23 10:45 AM

I was finally able to get access.

The e-mail from MyGet was buried in spam

 

Once I claimed the feed, it seems to work

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 5
David_Glasgow
Ensign David_Glasgow Ensign
Ensign

Posted: ‎2022-06-22 12:59 PM

0 Likes
4
3092
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-22 12:59 PM

A few other notes:

  • SmartConnector service fails to start.
  • When I attempt to download the 

    Schneider Electric SmartConnector Framework Developer's license

I do not see anything and have no idea what a Machine Thumbprint might be ???

Tags (1)
  • Tags:
  • english
Reply
ardak
ardak Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2022-06-22 11:17 PM

0 Likes
3
3065
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-22 11:17 PM

Hi! 

 

  • SmartConnector service fails to start.

Check the logs in C:\ProgramData\SmartConnector\Logs, they might have some information that can help you understand why.

 

The licensing is described in chapter 7 of the installation guide. Your thumbprint is accessed through the portal, and if the SmartConnector service doesn't start, you don't have access to it

 

About your nuget 403 issue:

I see you're a SE employee. You're probably having issues with the Schneider proxy, you'll have to check your nuget.config file (%appdata%\NuGet\NuGet.Config) to make sure the proxy settings match up with the proxy.

Tags (1)
  • Tags:
  • english
Reply
David_Glasgow
Ensign David_Glasgow Ensign
Ensign

Posted: ‎2022-06-23 08:03 AM . Last Modified: ‎2022-06-23 08:09 AM

0 Likes
2
3045
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-23 08:03 AM

I was able to get the SmartConnector service running after:
1) Uninstalling SmartConnector

2) Uninstalling SQL Express

3) Reboot

4) Reinstall SQL Express

5) Reinstall SmartConnector

 

Current Status:

  • SmartConnector Service Running
  • I can see the SmartConnector DB in the SQL Server Management Studio
  • Connected using sa account and pwd
  • Problem with MyGet = <string xmlns="http://schemas.microsoft.com/2003/10/Serialization/">The feed can not be accessed.</string>
  • Using https://www.myget.org/F/mongoose/auth/47301ae6-6ab4-4a3a-b0b2-98a31d0121ee/api/v2
  • Visual Studio can't access the NuGet packages

 

The following is my NuGet.config
<?xml version="1.0" encoding="utf-8"?>
<configuration>
<packageSources>
<add key="SmartConnector" value="https://www.myget.org/F/mongoose/auth/47301ae6-6ab4-4a3a-b0b2-98a31d0121ee/api/v2" />
<add key="Microsoft Visual Studio Offline Packages" value="C:\Program Files (x86)\Microsoft SDKs\NuGetPackages\" />
</packageSources>
<packageRestore>
<add key="enabled" value="True" />
<add key="automatic" value="True" />
</packageRestore>
<bindingRedirects>
<add key="skip" value="False" />
</bindingRedirects>
<packageManagement>
<add key="format" value="0" />
<add key="disabled" value="False" />
</packageManagement>
</configuration>

Tags (1)
  • Tags:
  • english
Reply
David_Glasgow
Ensign David_Glasgow Ensign
Ensign

Posted: ‎2022-06-23 10:45 AM

0 Likes
1
3032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-23 10:45 AM

I was finally able to get access.

The e-mail from MyGet was buried in spam

 

Once I claimed the feed, it seems to work

Tags (1)
  • Tags:
  • english
Reply
PiotrJakubczyk
Sisko PiotrJakubczyk Sisko
Sisko

Posted: ‎2022-09-03 10:54 AM

0 Likes
0
2517
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-03 10:54 AM

I also had 403 Forbidden error although it seemed to me that I was successfully claimed feed. To be sure that you claimed feed you need to be able to access this webpage. Check this twice. I also configured proxy for my nuget

 

smartconnector claimed feed.png

 

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore