Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82489members
350063posts

EWS server writeable ValueItems

SmartConnector Forum

Discussion of SmartConnector applications for integration of various other building management systems (BMS) into EcoStruxure Building Operation

Solved
mike_meirovitz
Commander
Commander
0 Likes
2
150

EWS server writeable ValueItems

Hi,

 

We are developing an EWS server. When we define a ValueItem as Writeable, and the value is manually modified by EBO user, how the EWS server gets a message about the new value?

 

Thank you.

 

Mike


Accepted Solutions
Nick-Iebba
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
1
144

Re: EWS server writeable ValueItems

What you would want to do is write a Custom EWS Server, and a custom SetValuesProcessor. Each request that is received from an EWS SOAP client to a native SmartConnector EWS Server is handled by a unique request processor; in this case, your "SetValuesProcessor" will provide custom handling for the "SetValues" method.

 

When you get a request sent to the server, you will know when values are changed. In that custom processor, when a successful SetValues happens, add custom logic to do what you want with that information.

See Answer In Context

2 Replies 2
Nick-Iebba
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
1
145

Re: EWS server writeable ValueItems

What you would want to do is write a Custom EWS Server, and a custom SetValuesProcessor. Each request that is received from an EWS SOAP client to a native SmartConnector EWS Server is handled by a unique request processor; in this case, your "SetValuesProcessor" will provide custom handling for the "SetValues" method.

 

When you get a request sent to the server, you will know when values are changed. In that custom processor, when a successful SetValues happens, add custom logic to do what you want with that information.

mike_meirovitz
Commander
Commander
0 Likes
0
138

Re: EWS server writeable ValueItems

Thank you Nick!

Mike